Hey guys that wasn't private. Just a heads up

On Tue, Sep 10, 2019 at 4:30 PM Skyler Bilbo via Sprinklerforum <
[email protected]> wrote:

> That would definitely get more water to a building... provide jobs and
> toilets for the homeless...
>
> I'm recruiting at a career fair right now. Despite low unemployment, there
> are a large number of older people here looking for a job. I'll give them
> your info too... I'm sure they wouldn't mind flushing toilets in sunny
> California ;)
>
> I hope all is well with you, buddy!
>
>
> -Skyler
>
>
> On Tue, Sep 10, 2019, 3:12 PM Parsley Consulting via Sprinklerforum <
> [email protected]> wrote:
>
>> Maybe we could hire a bunch of homeless people to run through a building
>> and flush all the toilets at the same time.  Sort of a man made undertow?
>>
>> Just thinking...
>>
>> *Ken Wagoner, SET Parsley Consulting*
>>
>>
>>
>> * 350 West 9th Avenue, Suite 206
>> <https://www.google.com/maps/search/350+West+9th+Avenue,+Suite+206+%0D%0A+++++++++++++Escondido,+California+92025?entry=gmail&source=g>
>> <https://www.google.com/maps/search/350+West+9th+Avenue,+Suite+206+%0D%0A+++++++++++++Escondido,+California+92025?entry=gmail&source=g>Escondido,
>> California 92025
>> <https://www.google.com/maps/search/350+West+9th+Avenue,+Suite+206+%0D%0A+++++++++++++Escondido,+California+92025?entry=gmail&source=g>
>> Phone 760-745-6181 Visit the website <http://www.parsleyconsulting.com/> *
>> On 09/10/2019 12:51 PM, Skyler Bilbo via Sprinklerforum wrote:
>>
>> I think it is worth pointing out that the way our table reads in 13R, and
>> the way that the plumbing code sizes piping, uses fixture units to convert
>> to flow, which do not convert linearly. For example, if we had a building
>> with 100 fixture units, we would plug in a domestic demand of 45 GPM and
>> for a building with 1000 fixture units we would plug in a domestic
>> demand of 200 GPM (NOT 450 GPM). I believe this is done to account for the
>> fact that not all of the domestic fixtures are running at once.
>>
>> Back to the original question, here's what I would do (for what it is
>> worth).  Figure the domestic demand using the table for the new building
>> and add it at the point of connection. Then add together the fixture units
>> for both buildings, find the GPM value in the table, then deduct the GPM
>> that I already added for the new building. I would plug that GPM in for
>> domestic demand for the existing building at the point of connection.
>>
>> When multiple buildings are connected to the same, small, dead end main,
>> there can be a very real pressure drop due to domestic water usage (that's
>> why we go through this excersize in the first place). It's good to remember
>> that this isn't all theoretical. If something were to happen, I wouldn't
>> want it on my conscience that I purposefully didn't account for something
>> that I knew could be a real issue. If the water main is too small, then the
>> water main is too small.
>>
>> Also, I think it is worth mentioning that this may lead to a situation we
>> see all of the time with RPZ backflow preventers. When the pressure
>> fluctuates on the inlet side of the RPZ (in this case because of the
>> domestic demand), the relief will spray/dump and you will have a very angry
>> owner with water everywhere. If you are using a RPZ, put a check valve in
>> before the backflow to prevent this from ever happening. It is likely that
>> no one will know the disaster that would have been, except you. If the
>> backflow is a double check, this is not an issue.
>>
>>
>> Skyler Bilbo
>> Wente Plumbing and Fire Protection
>> 1700 S. Raney Street
>> <https://www.google.com/maps/search/1700+S.+Raney+Street+%0D%0A+++++++++++++Effingham,+IL+62401?entry=gmail&source=g>
>> Effingham, IL 62401
>> <https://www.google.com/maps/search/1700+S.+Raney+Street+%0D%0A+++++++++++++Effingham,+IL+62401?entry=gmail&source=g>
>>
>> <https://www.google.com/maps/search/1700+S.+Raney+Street+%0D%0A+++++++++++++Effingham,+IL+62401?entry=gmail&source=g>
>> 217-819-6404 Direct
>> 217-347-7315 Fax
>>
>>
>>
>> On Tue, Sep 10, 2019, 12:37 PM Pete Schwab via Sprinklerforum <
>> [email protected]> wrote:
>>
>>> Steve
>>>
>>> Codes cannot cover 100% of the exact situations that we will encounter
>>> in the real world. I submitted this proposal because we had Engineers and
>>> AHJ’s requiring domestic demand being added for all buildings attached to a
>>> site main.
>>>
>>> What is the likelihood of all the fixtures being used simultaneously
>>> during a fire event? What is the impact of not calculating that other
>>> building? 2-3 PSI? So we have a .047 Density verses a .05? Being 13R we are
>>> probably calculating a 4 sprinkler design whereas the UL 1626 test is 2
>>> sprinklers? The first operating sprinkler opens with the full available
>>> pressure verses the listing? I think we are picking the fly $h!t out of the
>>> pepper here……
>>>
>>> Just my opinion as a member of the Residential Committee and not that of
>>> the NFPA.
>>>
>>> Pete
>>>
>>>
>>>
>>> Peter Schwab
>>>
>>> VP of Purchasing and Engineering technologies
>>>
>>>
>>>
>>> Wayne Automatic Fire Sprinklers Inc.
>>>
>>> 222 Capitol Court
>>> <https://www.google.com/maps/search/222%0D%0A++++++++++++++++++++++Capitol+Court+%0D%0A+++++++++++++++++++Ocoee,%0D%0A++++++++++++++++++++++Fl+34761?entry=gmail&source=g>
>>>
>>> <https://www.google.com/maps/search/222%0D%0A++++++++++++++++++++++Capitol+Court+%0D%0A+++++++++++++++++++Ocoee,%0D%0A++++++++++++++++++++++Fl+34761?entry=gmail&source=g>
>>>
>>> Ocoee, Fl 34761
>>> <https://www.google.com/maps/search/222%0D%0A++++++++++++++++++++++Capitol+Court+%0D%0A+++++++++++++++++++Ocoee,%0D%0A++++++++++++++++++++++Fl+34761?entry=gmail&source=g>
>>>
>>>
>>>
>>> *Mobile: (407) 468-8248*
>>>
>>> Direct: (407) 877-5570
>>>
>>> Fax: (407) 656-8026
>>>
>>>
>>>
>>> www.waynefire.com
>>>
>>>
>>>
>>> [image: cid:[email protected]]
>>>
>>>
>>>
>>> [image: WAYNE_40thAnniversary (1)]
>>>
>>>
>>>
>>> *I sleep in a sprinklered home, do you? *
>>>
>>>
>>>
>>>
>>>
>>> *From:* Steve Leyton <[email protected]>
>>> *Sent:* Tuesday, September 10, 2019 11:14 AM
>>> *To:* Pete Schwab <[email protected]>;
>>> [email protected]
>>> *Cc:* J H <[email protected]>
>>> *Subject:* RE: 13R Fixture Units for Multiple Buildings
>>>
>>>
>>>
>>> Hey Pete:
>>>
>>> I do not recall the discussion specifically, but our intent was to not
>>> have to put in an 8” main because of the plumbing unit values in 13R and
>>> what the non-fire allowance would look like if you have 30 buildings on
>>> site using a common water supply.    The point of adding domestic allowance
>>> is to pad the water supply for non-fire uses.  It is counterintuitive to
>>> ignore the potential concurrent domestic and irrigation flows that could
>>> impact the fire sprinkler system water supply and in this case we should
>>> consider intent, which is to assure that the portion of the site piping
>>> that serves both buildings can accommodate all fire and non-fire flows.  In
>>> this example the calculation is being done on a satellite, not the main
>>> building on the parcel.
>>>
>>>
>>>
>>> SML
>>>
>>>
>>>
>>>
>>>
>>> *From:* Pete Schwab [mailto:[email protected] <[email protected]>]
>>> *Sent:* Tuesday, September 10, 2019 5:10 AMth
>>> *To:* [email protected]
>>> *Cc:* Steve Leyton; J H
>>> *Subject:* RE: 13R Fixture Units for Multiple Buildings
>>>
>>>
>>>
>>> I disagree with Steve on this one
>>>
>>> In my opinion, the intent is to only add domestic demand for *the
>>> building being calculated* regardless of the underground/feed
>>> arrangement.
>>>
>>> If there is another “building” connected to the underground, that
>>> domestic demand does not need to be added.
>>>
>>> Below is the ROP from when this language was added (2013 edition).
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>> Peter Schwab
>>>
>>> VP of Purchasing and Engineering technologies
>>>
>>>
>>>
>>> Wayne Automatic Fire Sprinklers Inc.
>>>
>>> 222 Capitol Court
>>> <https://www.google.com/maps/search/222%0D%0A++++++++++++++++++++++Capitol+Court+%0D%0A+++++++++++++++++++Ocoee,%0D%0A++++++++++++++++++++++Fl+34761?entry=gmail&source=g>
>>>
>>> <https://www.google.com/maps/search/222%0D%0A++++++++++++++++++++++Capitol+Court+%0D%0A+++++++++++++++++++Ocoee,%0D%0A++++++++++++++++++++++Fl+34761?entry=gmail&source=g>
>>>
>>> Ocoee, Fl 34761
>>> <https://www.google.com/maps/search/222%0D%0A++++++++++++++++++++++Capitol+Court+%0D%0A+++++++++++++++++++Ocoee,%0D%0A++++++++++++++++++++++Fl+34761?entry=gmail&source=g>
>>>
>>>
>>>
>>> *Mobile: (407) 468-8248*
>>>
>>> Direct: (407) 877-5570
>>>
>>> Fax: (407) 656-8026
>>>
>>>
>>>
>>> www.waynefire.com
>>>
>>>
>>>
>>> [image: cid:[email protected]]
>>>
>>>
>>>
>>> [image: WAYNE_40thAnniversary (1)]
>>>
>>>
>>>
>>> *I sleep in a sprinklered home, do you? *
>>>
>>>
>>>
>>>
>>>
>>> *From:* Sprinklerforum <[email protected]> *On
>>> Behalf Of *Steve Leyton via Sprinklerforum
>>> *Sent:* Monday, September 9, 2019 6:47 PM
>>> *To:* [email protected]
>>> *Cc:* Steve Leyton <[email protected]>; J H <
>>> [email protected]>
>>> *Subject:* RE: 13R Fixture Units for Multiple Buildings
>>>
>>>
>>>
>>> I think “for the building being calculated” doesn’t take into account
>>> the potential arrangement of a single water line supplying domestic and
>>> fire protection to multiple buildings.    If I was the AHJ, I would require
>>> the fixture load allowance of both buildings to be added to the sprinkler
>>> demand of the subject building for that portion of the piping that is
>>> common to both buildings.   So if you’re coming in from a meter to the main
>>> building and call that Section A, then you have Section B going to the
>>> Satellite building, I would calculate Satellite sprinkler demand +
>>> Satellite domestic allowance in Section B, then at the point where the line
>>> branches off to the main building I would add the Main building plumbing
>>> allowance so that Section A includes Satellite sprinkler demand plus
>>> Satellite domestic + Main Building  domestic.
>>>
>>> I hope that makes sense.
>>>
>>>
>>>
>>> Steve L.
>>>
>>>
>>>
>>> *From:* Sprinklerforum [
>>> mailto:[email protected]
>>> <[email protected]>] *On Behalf Of *J H
>>> via Sprinklerforum
>>> *Sent:* Monday, September 09, 2019 3:17 PM
>>> *To:* [email protected]
>>> *Cc:* J H
>>> *Subject:* 13R Fixture Units for Multiple Buildings
>>>
>>>
>>>
>>> I've got a Bed & Breakfast (sprinklered per 13R) that is building a
>>> second detached suite which is to likewise be sprinklered to 13R. The
>>> existing yard line supplies both the domestic and fire demands for the
>>> existing building and the new building is planned to also tap into this
>>> yard line.
>>>
>>>
>>>
>>> Question: In determining the fixture units for the new building would we
>>> also have to account for the existing building's fixture units when
>>> calculating back to the city tap?
>>>
>>>
>>>
>>> 13R states: "9.6* Domestic Demand  Domestic demand for the building
>>> being calculated shall be included as part of the overall system demand for
>>> systems with common domestic/fire mains where no provisions are made to
>>> prevent thedomestic waterflow upon sprinkler system activation."
>>>
>>>
>>>
>>> I think the keywords are "for the building being calculated" and we
>>> would not have to account for anything else but I'm also thinking that if
>>> the intent is to account for water losses due to domestic usage and we are
>>> daisy chaining off of a relatively small, private, water line that it would
>>> be wise to account for these losses.
>>>
>>>
>>>
>>> Any thoughts?
>>>
>>>
>>>
>>> JH
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>>
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>
>>
>> _______________________________________________
>> Sprinklerforum mailing 
>> [email protected]http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>>
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
-- 