Maybe we could hire a bunch of homeless people to run through a building and flush all the toilets at the same time.  Sort of a man made undertow?

Just thinking...
*Ken Wagoner, SET
*Parsley Consulting***
*350 West 9th Avenue, Suite 206
*Escondido, California 92025
*****Phone 760-745-6181*
Visit the website <http://www.parsleyconsulting.com/> ***
On 09/10/2019 12:51 PM, Skyler Bilbo via Sprinklerforum wrote:
I think it is worth pointing out that the way our table reads in 13R, and the way that the plumbing code sizes piping, uses fixture units to convert to flow, which do not convert linearly. For example, if we had a building with 100 fixture units, we would plug in a domestic demand of 45 GPM and for a building with 1000 fixture units we would plug in a domestic demand of 200 GPM (NOT 450 GPM). I believe this is done to account for the fact that not all of the domestic fixtures are running at once.

Back to the original question, here's what I would do (for what it is worth).  Figure the domestic demand using the table for the new building and add it at the point of connection. Then add together the fixture units for both buildings, find the GPM value in the table, then deduct the GPM that I already added for the new building. I would plug that GPM in for domestic demand for the existing building at the point of connection.

When multiple buildings are connected to the same, small, dead end main, there can be a very real pressure drop due to domestic water usage (that's why we go through this excersize in the first place). It's good to remember that this isn't all theoretical. If something were to happen, I wouldn't want it on my conscience that I purposefully didn't account for something that I knew could be a real issue. If the water main is too small, then the water main is too small.

Also, I think it is worth mentioning that this may lead to a situation we see all of the time with RPZ backflow preventers. When the pressure fluctuates on the inlet side of the RPZ (in this case because of the domestic demand), the relief will spray/dump and you will have a very angry owner with water everywhere. If you are using a RPZ, put a check valve in before the backflow to prevent this from ever happening. It is likely that no one will know the disaster that would have been, except you. If the backflow is a double check, this is not an issue.


Skyler Bilbo
Wente Plumbing and Fire Protection
1700 S. Raney Street
Effingham, IL 62401
217-819-6404 Direct
217-347-7315 Fax



On Tue, Sep 10, 2019, 12:37 PM Pete Schwab via Sprinklerforum <[email protected] <mailto:[email protected]>> wrote:

    Steve

    Codes cannot cover 100% of the exact situations that we will
    encounter in the real world. I submitted this proposal because we
    had Engineers and AHJ’s requiring domestic demand being added for
    all buildings attached to a site main.

    What is the likelihood of all the fixtures being used
    simultaneously during a fire event? What is the impact of not
    calculating that other building? 2-3 PSI? So we have a .047
    Density verses a .05? Being 13R we are probably calculating a 4
    sprinkler design whereas the UL 1626 test is 2 sprinklers? The
    first operating sprinkler opens with the full available pressure
    verses the listing? I think we are picking the fly $h!t out of the
    pepper here……

    Just my opinion as a member of the Residential Committee and not
    that of the NFPA.

    Pete

    Peter Schwab

    VP of Purchasing and Engineering technologies

    Wayne Automatic Fire Sprinklers Inc.

    222 Capitol Court

    Ocoee, Fl 34761

    *Mobile: (407) 468-8248*

    Direct: (407) 877-5570

    Fax: (407) 656-8026

    www.waynefire.com <http://www.waynefire.com/>

    cid:[email protected]

    WAYNE_40thAnniversary (1)

    */I sleep in a sprinklered home, do you? /*

    *From:*Steve Leyton <[email protected]
    <mailto:[email protected]>>
    *Sent:* Tuesday, September 10, 2019 11:14 AM
    *To:* Pete Schwab <[email protected]
    <mailto:[email protected]>>;
    [email protected]
    <mailto:[email protected]>
    *Cc:* J H <[email protected]
    <mailto:[email protected]>>
    *Subject:* RE: 13R Fixture Units for Multiple Buildings

    Hey Pete:

    I do not recall the discussion specifically, but our intent was to
    not have to put in an 8” main because of the plumbing unit values
    in 13R and what the non-fire allowance would look like if you have
    30 buildings on site using a common water supply. The point of
    adding domestic allowance is to pad the water supply for non-fire
    uses.  It is counterintuitive to ignore the potential concurrent
    domestic and irrigation flows that could impact the fire sprinkler
    system water supply and in this case we should consider intent,
    which is to assure that the portion of the site piping that serves
    both buildings can accommodate all fire and non-fire flows.  In
    this example the calculation is being done on a satellite, not the
    main building on the parcel.

    SML

    *From:*Pete Schwab [mailto:[email protected]]
    *Sent:* Tuesday, September 10, 2019 5:10 AMth
    *To:* [email protected]
    <mailto:[email protected]>
    *Cc:* Steve Leyton; J H
    *Subject:* RE: 13R Fixture Units for Multiple Buildings

    I disagree with Steve on this one

    In my opinion, the intent is to only add domestic demand for *_the
    building being calculated_*regardless of the underground/feed
    arrangement.

    If there is another “building” connected to the underground, that
    domestic demand does not need to be added.

    Below is the ROP from when this language was added (2013 edition).

    Peter Schwab

    VP of Purchasing and Engineering technologies

    Wayne Automatic Fire Sprinklers Inc.

    222 Capitol Court

    Ocoee, Fl 34761

    *Mobile: (407) 468-8248*

    Direct: (407) 877-5570

    Fax: (407) 656-8026

    www.waynefire.com <http://www.waynefire.com/>

    cid:[email protected]

    WAYNE_40thAnniversary (1)

    */I sleep in a sprinklered home, do you? /*

    *From:*Sprinklerforum
    <[email protected]
    <mailto:[email protected]>> *On
    Behalf Of *Steve Leyton via Sprinklerforum
    *Sent:* Monday, September 9, 2019 6:47 PM
    *To:* [email protected]
    <mailto:[email protected]>
    *Cc:* Steve Leyton <[email protected]
    <mailto:[email protected]>>; J H
    <[email protected] <mailto:[email protected]>>
    *Subject:* RE: 13R Fixture Units for Multiple Buildings

    I think “for the building being calculated” doesn’t take into
    account the potential arrangement of a single water line supplying
    domestic and fire protection to multiple buildings.    If I was
    the AHJ, I would require the fixture load allowance of both
    buildings to be added to the sprinkler demand of the subject
    building for that portion of the piping that is common to both
    buildings.   So if you’re coming in from a meter to the main
    building and call that Section A, then you have Section B going to
    the Satellite building, I would calculate Satellite sprinkler
    demand + Satellite domestic allowance in Section B, then at the
    point where the line branches off to the main building I would add
    the Main building plumbing allowance so that Section A includes
    Satellite sprinkler demand plus Satellite domestic + Main Building
     domestic.

    I hope that makes sense.

    Steve L.

    *From:*Sprinklerforum
    [mailto:[email protected]] *On Behalf
    Of *J H via Sprinklerforum
    *Sent:* Monday, September 09, 2019 3:17 PM
    *To:* [email protected]
    <mailto:[email protected]>
    *Cc:* J H
    *Subject:* 13R Fixture Units for Multiple Buildings

    I've got a Bed & Breakfast (sprinklered per 13R) that is building
    a second detached suite which is to likewise be sprinklered to
    13R. The existing yard line supplies both the domestic and fire
    demands for the existing building and the new building is planned
    to also tap into this yard line.

    Question: In determining the fixture units for the new building
    would we also have to account for the existing building's fixture
    units when calculating back to the city tap?

    13R states: "9.6* Domestic Demand  Domestic demand for the
    building being calculated shall be included as part of the overall
    system demand for systems with common domestic/fire mains where no
    provisions are made to prevent thedomestic waterflow upon
    sprinkler system activation."

    I think the keywords are "for the building being calculated" and
    we would not have to account for anything else but I'm also
    thinking that if the intent is to account for water losses due to
    domestic usage and we are daisy chaining off of a relatively
    small, private, water line that it would be wise to account for
    these losses.

    Any thoughts?

    JH

    _______________________________________________
    Sprinklerforum mailing list
    [email protected]
    <mailto:[email protected]>
    http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to