An insurance adjuster is telling a local packaging plant they need to update their current sprinkler system to meet the higher demands of product they are now storing. Adjuster is classifying everything as Unexpanded Group A plastics, on racks, max 25' storage, max 30' ceilings. One option allows .45/2500 + 500 hose using 11.2K heads. Running some quick numbers I'm around 1850 GPM @ 65 PSI. The latest flow test is only 84 Static, 60 Residual @ 1010 GPM. They've been told their gonna need a pump, I'm thinking they need more water as well. Thoughts?
Brian Harris, CET BVS Systems Inc. Design Manager bvssystemsinc.com<http://bvssystemsinc.com/> Phone: 704.896.9989 Fax: 704.896.1935