Hey Ken-
NFPA-13 (2013) 15.2.2 lead me to 15.2.6

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com<http://bvssystemsinc.com/>

From: Sprinklerforum <[email protected]> On Behalf 
Of Parsley Consulting via Sprinklerforum
Sent: Thursday, September 12, 2019 11:43 AM
To: [email protected]
Cc: Parsley Consulting <[email protected]>
Subject: Re: Pump? Or Pump & Tank?

And to add on to what Steve noted - there are always four considerations - at 
least - when protecting storage.  The ones I use:

  1.  What is being stored?
     *   If it's plastic, is it in cartons or exposed?
  2.  How is it being stored? Racks? (single, double, multiple?) Pallets?  
Shelf?
     *    Is it encapsulated? Not really an issue when protecting plastics 
however.
  3.  How high is the intended/possible storage?

  4.  How high is the ceiling above the top of the storage?

There are any number of other considerations such as roof slope.  Until you 
have all that data any approach in protecting storage is incomplete.

Also, I looked into chapter 17 for storage of plastics up to 25' in racks, and 
I didn't find one which had a remote area of 2,500 ft² and a density of 0.45.  
Where did you come up with 0.45/2500?
Ken Wagoner, SET
Parsley Consulting
350 West 9th Avenue, Suite 206
Escondido, California 92025
Phone 760-745-6181
Visit the website<http://www.parsleyconsulting.com/>
On 09/12/2019 8:12 AM, Steve Leyton via Sprinklerforum wrote:
Do you know how to do a flow rate projection from a two point flow test?    I 
figure that with overflow your .45/2500 will require 1250 GPM + 500 GPM hose, 
yes?   At 1750 GPM your flow test projects to a residual pressure of 22-23 PSI, 
so you don't need a tank but you do need a pump.

Steve L.

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Brian Harris via Sprinklerforum
Sent: Thursday, September 12, 2019 8:08 AM
To: 
[email protected]<mailto:[email protected]>
Cc: Brian Harris
Subject: Pump? Or Pump & Tank?

An insurance adjuster is telling a local packaging plant they need to update 
their current sprinkler system to meet the higher demands of product they are 
now storing. Adjuster is classifying everything as Unexpanded Group A plastics, 
on racks, max 25' storage, max 30' ceilings. One option allows .45/2500 + 500 
hose using 11.2K heads. Running some quick numbers I'm around 1850 GPM @ 65 
PSI. The latest flow test is only 84 Static, 60 Residual @ 1010 GPM. They've 
been told their gonna need a pump, I'm thinking they need more water as well. 
Thoughts?


Brian Harris, CET
BVS Systems Inc.
Design Manager
bvssystemsinc.com<http://bvssystemsinc.com/>
Phone: 704.896.9989
Fax: 704.896.1935




_______________________________________________

Sprinklerforum mailing list

[email protected]<mailto:[email protected]>

http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to