Do you know how to do a flow rate projection from a two point flow test?    I 
figure that with overflow your .45/2500 will require 1250 GPM + 500 GPM hose, 
yes?   At 1750 GPM your flow test projects to a residual pressure of 22-23 PSI, 
so you don't need a tank but you do need a pump.

Steve L.

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Brian Harris via Sprinklerforum
Sent: Thursday, September 12, 2019 8:08 AM
To: [email protected]
Cc: Brian Harris
Subject: Pump? Or Pump & Tank?

An insurance adjuster is telling a local packaging plant they need to update 
their current sprinkler system to meet the higher demands of product they are 
now storing. Adjuster is classifying everything as Unexpanded Group A plastics, 
on racks, max 25' storage, max 30' ceilings. One option allows .45/2500 + 500 
hose using 11.2K heads. Running some quick numbers I'm around 1850 GPM @ 65 
PSI. The latest flow test is only 84 Static, 60 Residual @ 1010 GPM. They've 
been told their gonna need a pump, I'm thinking they need more water as well. 
Thoughts?


Brian Harris, CET
BVS Systems Inc.
Design Manager
bvssystemsinc.com<http://bvssystemsinc.com/>
Phone: 704.896.9989
Fax: 704.896.1935

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
  • Pump? Or Pump &... Brian Harris via Sprinklerforum
    • RE: Pump? Or ... Steve Leyton via Sprinklerforum
      • Re: Pump?... Parsley Consulting via Sprinklerforum
        • RE: P... Brian Harris via Sprinklerforum
          • R... Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
      • RE: Pump?... Prahl, Craig/GVL via Sprinklerforum
    • Re: Pump? Or ... Jeff Normand via Sprinklerforum

Reply via email to