2013 NFPA 72 Chapter 7 details the documentation requirements [including those for shop drawings in the subsections of Section 7.4]. Be sure to read the corresponding annex sections for Ch.7. I recommend using the handbook so you also get to read the NFPA commentary information to achieve a better understanding.
Respectfully, David Blackwell David Blackwell, P.E. Chief Engineer (803)896-9833 Office of State Fire Marshal 141 Monticello Trail | Columbia, SC 29203 http://statefire.llr.sc.gov/ (803)896-9800 "Our firefighting starts with plan review..." From: Sprinklerforum <[email protected]> On Behalf Of John Irwin via Sprinklerforum Sent: Wednesday, October 23, 2019 1:10 PM To: [email protected] Cc: John Irwin <[email protected]> Subject: Fire Alarm plan checklist *** SCDLLR NOTICE *** * This email is from an external email address. Please use caution when deciding whether to open any attachments or when clicking links. * Personally Identifiable Information (PII) should not be included in e-mail text or attachments. Do not save or transmit PII unencrypted. We have chapter 23 in NFPA 13 that gives us our checklist of what needs to be included in our shop drawings. Is there are similar check list for fire alarms? I don't see anything in NFPA 72 John Irwin
_______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org