The most I've seen is from A.3.3.251:

   /Shop Drawings. Shop drawings typically include the property
   location, scaled//floor plans, equipment wiring details, typical
   equipment installation details, riser details, conduit///conductor
   size, and routing information needed to install a fire alarm and/or
   signaling//system./

and in item (3) of A.7.2.1:

   /(3) Floor plan layout showing locations of all devices, control
   equipment, and supervising station and shared communications
   equipment with each sheet showing the following:
   /

       /(a) Point of compass (north arrow)//
       //(b) A graphic representation of the scale used//
       //(c) Room use identification//
       //(d) Building features that will affect the placement of
       initiating devices and notification appliances/

See also 7.4.5, and 7.4.6:/
/

   /7.4.5 Floor plan drawings shall be drawn to an indicated scale and
   shall include the following information, where applicable for the
   particular system:
   /

       /(1) Floor or level identification
       (2) Point of compass (indication of North)
       (3) Graphic scale
       (4) All walls and doors
       (5) All partitions extending to within 15 percent of the ceiling
       height (where applicable and when known)
       (6) Room and area descriptions
       (7) System devices/component locations
       (8) Locations of fire alarm primary power disconnecting means
       (9) Locations of monitor/control interfaces to other systems
       (10) System riser locations
       (11) Type and number of system components/devices on each
       circuit, on each floor or level
       (12) Type and quantity of conductors and conduit (if used) for
       each circuit
       (13) Identification of any ceiling over 10 ft (3.0 m) in height
       where automatic fire detection is being proposed
       (14) Details of ceiling geometries, including beams and solid
       joists, where automatic fire detection is being proposed
       (15) Where known, acoustic properties of spaces
       /

   /7.4.6 System riser diagrams shall be coordinated with the floor
   plans and shall include the following information:
   /

       /(1) General arrangement of the system in building cross-section
       (2) Number of risers
       (3) Type and number of circuits in each riser
       (4) Type and number of system components/devices on each
       circuit, on each floor or level
       (5) Number of conductors for each circuit
       /

That is all from the 2016 edition of -72.
*Ken Wagoner, SET
*Parsley Consulting***
*350 West 9th Avenue, Suite 206
*Escondido, California 92025
*****Phone 760-745-6181*
Visit the website <http://www.parsleyconsulting.com/>

***
On 10/23/2019 10:10 AM, John Irwin via Sprinklerforum wrote:

We have chapter 23 in NFPA 13 that gives us our checklist of what needs to be included in our shop drawings.

Is there are similar check list for fire alarms? I don’t see anything in NFPA 72

John Irwin


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to