I just ran into a somewhat similar situation last week. It seems like you are forgetting something major. It is very likely that you have to install sprinklers below the mezzanine floor. Unless I'm wrong, this counts as an obstruction over 4 ft in width for standard spray sprinklers, and I can't think of anything in the CMSA or ESFR chapters/sections that would allow you to not install sprinklers under that mezzanine floor.
Skyler Bilbo 1700 S. Raney Street Effingham, IL 62401 217-819-6404 Direct 217-347-7315 Fax [email protected] www.wenteplumbing.com On Wed, Dec 11, 2019 at 8:13 AM Micah Davis, SET via Sprinklerforum < [email protected]> wrote: > I am working on a car dealership with a service shop. There is a 2,285 sf > parts storage area in the middle of the building. This area has a > mezzanine at 10'-6" AFF. The engineer specified protection in accordance > with NFPA 13 - Table 20.2 which requires 16 K25 sprinklers at 37 psi. This > equals over 2400 GPM and is well above the available water supply. I > believe this protection is overkill for a couple of reasons: > > 1. We have no where near 25 ft of storage height since we have two > levels. One is a total of 10'-6" and the second has a max ceiling height > of 10'-11". > 2. The selected table specifies portable racks (closed array) which > does not describe a typical parts storage area with fixed shelves and > aisles. > > I have brought this to the design team's attention and they have asked for > a recommendation. Setting aside the, 'this is the engineer's job' > conversation which I have had with them, I could use some input from the > wisdom of the forum to make sure I am on the right track. I'm following > the engineer's thought with the Group A plastics mainly because I don't > have all the commodity info I need and I'm looking at CMSA sprinklers. The > minimum protection scheme available is for 20 ft storage and 25 ft max > ceiling height. I'm choosing 15 K16.8 sprinklers at 22 PSI. > > My concern is the clearance to storage. Based on the measurements shown > in the screenshot below, with the 36" clearance requirement the max storage > height I'm sure will be much lower than the shelving they will install in > this space. > > I know this is not an uncommon arrangement, so I'm sure this has been > worked out by people much smarter than me. Am I missing something in all > of this? > > > > Micah Davis, SET > NICET #124745 > Water Based Systems Layout, Level IV Dynamic Fire Designs > > *Mail: [email protected] <[email protected]>* > Mobile: 931-242-1299 > www.dynamicfiredesigns.com <http://dynamicfiredesigns.com/> > > Dynamic Fire Designs • 247 Winthrop Dr. • Spring Hill • FL • 34609 > > This message is confidential. It may also be privileged or otherwise > protected by work product immunity or other legal rules. If you have > received it by mistake, please let us know by e-mail reply and delete it > from your system; you may not copy this message or disclose its contents to > anyone. The integrity and security of this message cannot be guaranteed on > the Internet. > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org >
_______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org