I'd suggest taking a look at Chapter 13, Miscellaneous and Low-Piled storage 
since you have two levels where the height of the storage is less than 12 ft.  
on each level.

Craig Prahl | Jacobs | Group Lead/SME - Fire Protection | 864.676.5252 | 
[email protected]<mailto:[email protected]> | 
www.jacobs.com<http://www.jacobs.com/>
1041 East Butler Road   Greenville, South Carolina  29606

From: Sprinklerforum <[email protected]> On Behalf 
Of Micah Davis, SET via Sprinklerforum
Sent: Wednesday, December 11, 2019 10:59 AM
To: [email protected]
Cc: Micah Davis, SET <[email protected]>
Subject: [EXTERNAL] Re: Auto Parts Storage

Thank you all for the input.  I had not overlook the multiple levels, but I was 
having trouble finding the section of 13 that applied to my specific situation. 
 I think what I was missing was that I am dealing with shelf storage as 
addressed in Chapter 15 and not rack storage as addressed in Chapter 17.  I 
will try to confirm the type of storage (bins, boxes, or shelves) to be certain 
of which selection from chart 15.2.6(a) I need to select.  Thank you again!!

Micah Davis, SET
NICET #124745
Water Based Systems Layout, Level IV
Dynamic Fire Designs

Mail: [email protected]<mailto:[email protected]>
Mobile: 931-242-1299
www.dynamicfiredesigns.com<https://urldefense.com/v3/__http:/dynamicfiredesigns.com/__;!!B5cixuoO7ltTeg!WLLFvBTEdzxISHIDZN4sHuQBKfq770bpk0QG6lU2uwYTOEHc0FpKu2Z8CwWklHbQWg$>

Dynamic Fire Designs * 247 Winthrop Dr. * Spring Hill * FL * 34609

This message is confidential. It may also be privileged or otherwise protected 
by work product immunity or other legal rules. If you have received it by 
mistake, please let us know by e-mail reply and delete it from your system; you 
may not copy this message or disclose its contents to anyone. The integrity and 
security of this message cannot be guaranteed on the Internet.

________________________________
From: Prahl, Craig/GVL <[email protected]<mailto:[email protected]>>
Sent: Wednesday, December 11, 2019 10:30 AM
To: 
[email protected]<mailto:[email protected]>
 
<[email protected]<mailto:[email protected]>>
Cc: Micah Davis, SET <[email protected]<mailto:[email protected]>>
Subject: RE: Auto Parts Storage


You have TWO levels of storage that are less than 12 ft in height EACH.  Not 
ONE storage level of 20 ft.



Look at each level, provide sprinklers below the mezzanine and at the 
roof/ceiling above the mezzanine.



I'm wondering if the mezzanine decking is grating or solid because some 
"engineerz" think that grating doesn't count as a floor.



Is the storage bin type storage or boxes on shelves or what?  You need to know 
that.  Most parts are going to be plastic , rubber or metal or a combination of 
any of those or all of those.



Craig Prahl | Jacobs | Group Lead/SME - Fire Protection | 864.676.5252 | 
[email protected]<mailto:[email protected]> | 
www.jacobs.com<http://www.jacobs.com/>

1041 East Butler Road   Greenville, South Carolina  29606



From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 On Behalf Of Micah Davis, SET via Sprinklerforum
Sent: Wednesday, December 11, 2019 9:13 AM
To: SprinklerForum 
<[email protected]<mailto:[email protected]>>
Cc: Micah Davis, SET <[email protected]<mailto:[email protected]>>
Subject: [EXTERNAL] Auto Parts Storage



I am working on a car dealership with a service shop.  There is a 2,285 sf 
parts storage area in the middle of the building.  This area has a mezzanine at 
10'-6" AFF.  The engineer specified protection in accordance with NFPA 13 - 
Table 20.2 which requires 16 K25 sprinklers at 37 psi.  This equals over 2400 
GPM and is well above the available water supply.  I believe this protection is 
overkill for a couple of reasons:

  1.  We have no where near 25 ft of storage height since we have two levels.  
One is a total of 10'-6" and the second has a max ceiling height of 10'-11".
  2.  The selected table specifies portable racks (closed array) which does not 
describe a typical parts storage area with fixed shelves and aisles.

I have brought this to the design team's attention and they have asked for a 
recommendation.  Setting aside the, 'this is the engineer's job' conversation 
which I have had with them, I could use some input from the wisdom of the forum 
to make sure I am on the right track.  I'm following the engineer's thought 
with the Group A plastics mainly because I don't have all the commodity info I 
need and I'm looking at CMSA sprinklers.  The minimum protection scheme 
available is for 20 ft storage and 25 ft max ceiling height.  I'm choosing 15 
K16.8 sprinklers at 22 PSI.



My concern is the clearance to storage.  Based on the measurements shown in the 
screenshot below, with the 36" clearance requirement the max storage height I'm 
sure will be much lower than the shelving they will install in this space.



I know this is not an uncommon arrangement, so I'm sure this has been worked 
out by people much smarter than me.  Am I missing something in all of this?



[cid:[email protected]]



Micah Davis, SET
NICET #124745
Water Based Systems Layout, Level IV

Dynamic Fire Designs



Mail: [email protected]<mailto:[email protected]>
Mobile: 931-242-1299
www.dynamicfiredesigns.com<https://urldefense.com/v3/__http:/dynamicfiredesigns.com/__;!!B5cixuoO7ltTeg!WI4MsCvdJp-N9y4s7QWQUKe8Uj5UmYNA6LrqRbRPz-brXCjAMnG06eubMn-oY-bOQA$>

Dynamic Fire Designs * 247 Winthrop Dr. * Spring Hill * FL * 34609

This message is confidential. It may also be privileged or otherwise protected 
by work product immunity or other legal rules. If you have received it by 
mistake, please let us know by e-mail reply and delete it from your system; you 
may not copy this message or disclose its contents to anyone. The integrity and 
security of this message cannot be guaranteed on the Internet.



________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.

________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to