Look at Table 15.2.6(a) in the 2013 edition of 13.  That should cover
widgets in a box.  

 


Nick Maneen, SET 

c 704.791.7789

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Micah Davis, SET via Sprinklerforum
Sent: Wednesday, December 11, 2019 9:13 AM
To: SprinklerForum
Cc: Micah Davis, SET
Subject: Auto Parts Storage

 

I am working on a car dealership with a service shop.  There is a 2,285 sf
parts storage area in the middle of the building.  This area has a mezzanine
at 10'-6" AFF.  The engineer specified protection in accordance with NFPA 13
- Table 20.2 which requires 16 K25 sprinklers at 37 psi.  This equals over
2400 GPM and is well above the available water supply.  I believe this
protection is overkill for a couple of reasons:

1.      We have no where near 25 ft of storage height since we have two
levels.  One is a total of 10'-6" and the second has a max ceiling height of
10'-11".
2.      The selected table specifies portable racks (closed array) which
does not describe a typical parts storage area with fixed shelves and
aisles.

I have brought this to the design team's attention and they have asked for a
recommendation.  Setting aside the, 'this is the engineer's job'
conversation which I have had with them, I could use some input from the
wisdom of the forum to make sure I am on the right track.  I'm following the
engineer's thought with the Group A plastics mainly because I don't have all
the commodity info I need and I'm looking at CMSA sprinklers.  The minimum
protection scheme available is for 20 ft storage and 25 ft max ceiling
height.  I'm choosing 15 K16.8 sprinklers at 22 PSI.

 

My concern is the clearance to storage.  Based on the measurements shown in
the screenshot below, with the 36" clearance requirement the max storage
height I'm sure will be much lower than the shelving they will install in
this space.  

 

I know this is not an uncommon arrangement, so I'm sure this has been worked
out by people much smarter than me.  Am I missing something in all of this?


 



 


Micah Davis, SET
NICET #124745
Water Based Systems Layout, Level IV 

Dynamic Fire Designs


 


Mail: [email protected]
Mobile: 931-242-1299
www.dynamicfiredesigns.com <http://dynamicfiredesigns.com/>  


Dynamic Fire Designs . 247 Winthrop Dr. . Spring Hill . FL . 34609

This message is confidential. It may also be privileged or otherwise
protected by work product immunity or other legal rules. If you have
received it by mistake, please let us know by e-mail reply and delete it
from your system; you may not copy this message or disclose its contents to
anyone. The integrity and security of this message cannot be guaranteed on
the Internet. 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to