There are countless sections in the IBC that say sprinklers shall be  " . .
.installed throughout . ." or ". . .provided throughout . ." or  ".
.equipped throughout . ." or something similar.  But I don't' see where the
IBC tells me what "throughout" means.  I've assumed it meant sprinklers in
all areas that the applicable NFPA standard (NFPA 13 in this case) requires
them, but not in areas that the applicable NFPA standard allows them to be
omitted.  I've learned, since the IBC doesn't define the term, there are
jurisdictions that define it differently - more specifically they don't
recognize the omissions that NFPA 13 allows, only the exempt locations
listed in IBC section 903.3.1.1.1.  

 

Is anyone aware of an IBC document that would shed some light on this?  I've
found a number of articles from consultants, associations, etc., but
something directly from the IBC would carry a lot more weight.

 

Ed Kramer

Bamford Fire Sprinkler

 