Correct, throughout doesn't mean adding sprinklers to every sq. inch in order 
to comply with the literal term "throughout".  It applies to areas where the 
code requires them to be.

Taking an alternative approach is in compliance with the standard when approved 
by the AHJ and this is also disussed in greater length in the Commentary.  The 
point was that while you can use an alternative non-sprinkler approach and 
still be code compliant per section 904.2 (2015 IFC), you lose any and all 
advantages attributed with being sprinklered throughout.

My hands are beginning to cramp from typing throughout so many times throughout 
the course of this sprinklered throughout discussion.

Craig Prahl | Jacobs | Group Lead/SME - Fire Protection | 864.676.5252 | 
[email protected]<mailto:[email protected]> | 
www.jacobs.com<http://www.jacobs.com/>
1041 East Butler Road   Greenville, South Carolina  29606

From: Nick Maneen <[email protected]>
Sent: Thursday, January 30, 2020 3:34 PM
To: [email protected]
Cc: Prahl, Craig/GVL <[email protected]>; 'Ed Kramer' 
<[email protected]>
Subject: RE: [EXTERNAL] IBC "throughout"

To clarify, because I think many misunderstand this, throughout would be in 
accordance with the appropriate standard.  For example, it would not require 
additional sprinklers in pantries in a 13R building or sprinklers above a 
ceiling in a non-combustible 13 building.  I have had AHJs in the past try to 
start adding sprinklers where the standard allows them to be omitted because 
they don't understand.

Taking the exception for alternate means of protection that Craig mentions 
below may be fine with the adopted fire code and local AHJ but it is not in 
compliance with the standard.

Nick Maneen, SET
c 704.791.7789

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Prahl, Craig/GVL via Sprinklerforum
Sent: Thursday, January 30, 2020 3:17 PM
To: 
[email protected]<mailto:[email protected]>
Cc: Prahl, Craig/GVL; Ed Kramer
Subject: RE: [EXTERNAL] IBC "throughout"

When the IBC/IFC doesn't provide a specific definition we are told (ref. 2018 
IFC) 201.4 Terms not defined. Where terms are not defined
through the methods authorized by this section, such terms shall have 
ordinarily accepted meanings such as the context implies. Merriam Webster's 
Collegiate Dictionary, 11th Edition, shall be considered as providing 
ordinarily accepted meanings.

Throughout means throughout.

We've just been through this definition issue with a local architect.  Omission 
of sprinklers in a Control room with Sapphire provided is acceptable as an 
alternative by the AHJ but the building loses all advantages or allowances that 
are given to a fully sprinklered building since taking out sprinklers and 
substituting a gaseous system no longer qualifies as being sprinklered 
throughout.  Basically any part of the code that allows you to do something a 
little more risky or bigger, higher, wider or of greater quantity or whatever 
based on a fully sprinklered building or where sprinklers are installed 
throughout, now goes away and you can't do those things.

The Commentary spells this out in great detail.  2018, IFC Commentary, 903.1.1.

Craig Prahl | Jacobs | Group Lead/SME - Fire Protection | 864.676.5252 | 
[email protected]<mailto:[email protected]> | 
www.jacobs.com<http://www.jacobs.com/>
1041 East Butler Road   Greenville, South Carolina  29606

From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 On Behalf Of Ed Kramer via Sprinklerforum
Sent: Thursday, January 30, 2020 2:38 PM
To: 
[email protected]<mailto:[email protected]>
Cc: Ed Kramer <[email protected]<mailto:[email protected]>>
Subject: [EXTERNAL] IBC "throughout"

There are countless sections in the IBC that say sprinklers shall be  " . . 
.installed throughout . ." or ". . .provided throughout . ." or  ". .equipped 
throughout . ." or something similar.  But I don't' see where the IBC tells me 
what "throughout" means.  I've assumed it meant sprinklers in all areas that 
the applicable NFPA standard (NFPA 13 in this case) requires them, but not in 
areas that the applicable NFPA standard allows them to be omitted.  I've 
learned, since the IBC doesn't define the term, there are jurisdictions that 
define it differently - more specifically they don't recognize the omissions 
that NFPA 13 allows, only the exempt locations listed in IBC section 
903.3.1.1.1.

Is anyone aware of an IBC document that would shed some light on this?  I've 
found a number of articles from consultants, associations, etc., but something 
directly from the IBC would carry a lot more weight.

Ed Kramer
Bamford Fire Sprinkler


________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.

________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to