That doesn't sound legit - I would keep the tee in the calculations. A
bushing isn't really recognized as a fitting per table 23.4.3.1.1 - more
like a transient fitting.

On Tue, Feb 4, 2020 at 1:22 PM Kyle.Montgomery via Sprinklerforum <
[email protected]> wrote:

> Esteemed members of the fire sprinkler community,
>
>
>
> NFPA 13 (2016 Edition) section 8.15.20 is basically telling us to provide
> bushed 1” outlets for sprinklers in shell spaces, right?
>
>
>
> Section 23.4.4.8.1(9) tells us that friction loss can be excluded for the
> fitting directly connected to a sprinkler.
>
>
>
> In your opinion(s), is it the intent of the standard that you have to add
> the friction loss for a tee into your hydraulic calculation if using
> bushings, since the sprinkler is no longer directly connected to the tee?
> Or is it acceptable to consider a tee with a bushing as one fitting for the
> purpose of hydraulic calculations.
>
>
>