K-17. That’s a little different than I expect. I always thought more like parts 
of a strip mall building that might end up OH-2.

Best.

> On Feb 5, 2020, at 07:58, Kyle.Montgomery via Sprinklerforum 
> <sprinklerforum@lists.firesprinkler.org> wrote:
> 
> That’s the crux of my question. A literal interpretation could say that the 
> sprinkler is no longer connected directly to the tee, so you have to include 
> the equivalent length for the tee in the calculations. But is that really the 
> intent in this scenario? Is the bushing really creating an impact to the 
> hydraulics? It seems strange to me that the type of fitting the sprinkler is 
> connected to (welded outlet, threaded tee,  threaded elbow) is of no concern 
> to the hydraulics, unless the fitting has a bushed outlet. Does a threaded 
> tee with a bushing really create more friction loss than, say a saddle tee 
> (mechanical tee)?
>  
> In a lot of cases it doesn’t make much of a difference, but every once in a 
> while you run into a scenario where you’re upgrading an area that had 1” 
> outlets to something that needs a large orifice sprinkler (like a K17) and if 
> you have to add the friction loss for a 1” tee into your calc it really does 
> have an impact.
>  
> -Kyle M
>  
> From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] 
> On Behalf Of J H via Sprinklerforum
> Sent: Tuesday, February 4, 2020 3:41 PM
> To: sprinklerforum@lists.firesprinkler.org
> Cc: J H <design.azfire...@gmail.com>
> Subject: [EXTERNAL] Re: Shell Spaces and Bushed Outlets
>  
> That doesn't sound legit - I would keep the tee in the calculations. A 
> bushing isn't really recognized as a fitting per table 23.4.3.1.1 - more like 
> a transient fitting.
>  
> On Tue, Feb 4, 2020 at 1:22 PM Kyle.Montgomery via Sprinklerforum 
> <sprinklerforum@lists.firesprinkler.org> wrote:
> Esteemed members of the fire sprinkler community,
>  
> NFPA 13 (2016 Edition) section 8.15.20 is basically telling us to provide 
> bushed 1” outlets for sprinklers in shell spaces, right?
>  
> Section 23.4.4.8.1(9) tells us that friction loss can be excluded for the 
> fitting directly connected to a sprinkler.
>  
> In your opinion(s), is it the intent of the standard that you have to add the 
> friction loss for a tee into your hydraulic calculation if using bushings, 
> since the sprinkler is no longer directly connected to the tee? Or is it 
> acceptable to consider a tee with a bushing as one fitting for the purpose of 
> hydraulic calculations.
>  
> Kyle Montgomery
>  <image001.png>
> Aero Automatic Sprinkler Co.
> 21605 N. Central Ave.
> Phoenix, AZ 85024
> Direct: 623.580.7820
> Cell: 602.763.4736
> kmontgom...@aerofire.com
>  
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to