NFPA 13, 2016 ed. States:

23.4.4.2.5   Where the total design discharge from these oper-

ating sprinklers is less than the minimum required discharge

determined by multiplying the required design density times

the required minimum design area, an additional flow shall be

added at the point of connection of the branch line to the

cross main furthest from the source to increase the overall

demand, not including hose stream allowance, to the mini-

mum required discharge.

 

This is kinda gray to me.  Does it mean that if I have a light hazard area
that is only 884 sf (offices in a shop)

and the area modifier being applied will allow for a 900 sf area, then I
would need a minimum discharge of 90 gpm over the entire area?

Then, if my calculations bare out 92 gpm nothing else needs done, but if
they came out to 84 gpm an additional flow of 6 gpm would need to be added?

 

Sorry about the run on sentences, just confused.

 

 

Thank you,

 

Bob Knight, CET III

Fire by Knight, LLC

208-318-3057

FBK-LOGO-EMAIL

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
  • Floor area less th... Bob Knight via Sprinklerforum
    • Re: Floor are... Shawn Foor via Sprinklerforum
      • RE: Floor... Bob Knight via Sprinklerforum
        • RE: [... Kyle.Montgomery via Sprinklerforum
          • R... Bob Knight via Sprinklerforum
            • ... Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
              • ... Bob Knight via Sprinklerforum
                • ... Fpdcdesign via Sprinklerforum
                • ... Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
                • ... Bob Knight via Sprinklerforum
                • ... Jussef Liban - GRUPO 3S via Sprinklerforum

Reply via email to