14 K8.0 sprinklers at 7 psi calculates to min 296 gallons.   
  

  
  
  

  
  
>   
> On Jun 16, 2020 at 7:49 PM,  <Bob Knight via Sprinklerforum 
> (mailto:[email protected])>  wrote:
>   
>   
>           
>   
>
>  The spec is demanding 8.0K for the LH areas.
>
>   
>
>     
>
>   
>   
>
>     
>
>   
>
>  Thank you,
>
>   
>
>     
>
>   
>
>  Bob Knight, CET III
>
>   
>
>  Fire by Knight, LLC
>
>   
>
>  208-318-3057
>
>   
>   
>
>     
>
>   
>   
>   
>
>  From:    Sprinklerforum 
> [mailto:[email protected]]  On Behalf Of  Travis 
> Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
>   Sent:  Tuesday, June 16, 2020 5:48 PM
>   To:  [email protected]; [email protected]
>   Cc:  Travis Mack, SET, CFPS, CWBSP, RME-G
>   Subject:  RE: [EXTERNAL] RE: Floor area less than required
>
>   
>   
>   
>
>   
>
>   
>
>  4.2k or even 2.8k can be your friend – if applicable.
>
>   
>
>     
>
>   
>
>   (http://www.mfpdesign.com/)
>
>   
>
>  Travis Mack, CFPS, CWBSP, RME-G, SET
>
>   
>
>  Engineering Manager
>
>   
>
>  MFP Design
>
>   
>
>  3356 E Vallejo Ct
>
>   
>
>  Gilbert, AZ 85298
>
>   
>
>  NEW EXTENSION: 480-505-9271 ext. 700
>
>   
>
>  NEW MOBILE: 480-272-2471
>
>   
>
>    [email protected] (mailto:[email protected])
>
>   
>
>    [email protected] (mailto:[email protected])
>
>   
>
>  www.mfpdesign.com
>
>   
>
>     
>
>   
>
>  Send large files to us via:        https://www.hightail.com/u/MFPDesign 
> (https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0)
>      
>
>   
>
>  LinkedIn:        https://www.linkedin.com/in/travismack 
> (https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0)
>
>   
>
>     
>
>   
>
>  “The bitterness of poor quality remains long after the sweetness of low 
> price is forgotten.”
>
>   
>
>     
>
>   
>
>    Need/Want a faster way to check material pricing?    Build a material 
> quote?    Check availability ?      Searching for an invoice?
>
>   
>
>    *If you do not already have an account with ferguson.com, click   here 
> (https://www.ferguson.com/account-registration)   to register.*
>
>   
>
>    **Have a Ferguson account? Download the Ferguson app for on-the-go access 
> to your favorite ferguson.com features.   Apple iOS devices 
> (http://fergusoncommunications.us.newsweaver.com/hq7bgesq7f/1qtklpp37l9byeftyuoy12/external?email=true&a=6&p=2591775&t=517003)
>    or Android devices 
> (http://fergusoncommunications.us.newsweaver.com/hq7bgesq7f/n1gewi5ud95byeftyuoy12/external?email=true&a=6&p=2591775&t=517003)**
>
>   
>
>     
>
>   
>
>     
>
>   
>
>     
>
>   
>   
>   
>
>  From:    Sprinklerforum  <[email protected]>   
> On Behalf Of  Bob Knight via Sprinklerforum
>   Sent:  Tuesday, June 16, 2020 4:34 PM
>   To:  [email protected]
>   Cc:  Bob Knight  <[email protected]>
>   Subject:  RE: [EXTERNAL] RE: Floor area less than required
>
>   
>   
>   
>
>   
>
>   
>
>  Yep, it’s actually 14 sprinklers.    Bunch of small compartments.
>
>   
>
>     
>
>   
>   
>
>     
>
>   
>
>  Thank you,
>
>   
>
>     
>
>   
>
>  Bob Knight, CET III
>
>   
>
>  Fire by Knight, LLC
>
>   
>
>  208-318-3057
>
>   
>   
>
>     
>
>   
>   
>   
>
>  From:    Sprinklerforum 
> [mailto:[email protected]]  On Behalf Of  
> Kyle.Montgomery via Sprinklerforum
>   Sent:  Tuesday, June 16, 2020 5:33 PM
>   To:   [email protected] (mailto:[email protected]);  
> [email protected] 
> (mailto:[email protected])
>   Cc:  Kyle.Montgomery
>   Subject:  RE: [EXTERNAL] RE: Floor area less than required
>
>   
>   
>   
>
>   
>
>   
>
>  That sounds correct.
>
>   
>
>     
>
>   
>
>  It seems strange that your calculation is over-discharging by more than 100% 
> though. Minimum discharge is 90 GPM and you’re discharging over 200 GPM? Do 
> you have like 13 sprinklers jammed into this area?
>
>   
>
>     
>
>   
>
>  -Kyle M
>
>   
>
>     
>
>   
>   
>   
>
>  From:    Sprinklerforum  <[email protected] 
> (mailto:[email protected])>   On Behalf Of  Bob 
> Knight via Sprinklerforum
>   Sent:  Tuesday, June 16, 2020 3:27 PM
>   To:   [email protected] 
> (mailto:[email protected])
>   Cc:  Bob Knight  <[email protected] (mailto:[email protected])>
>   Subject:  [EXTERNAL] RE: Floor area less than required
>
>   
>   
>   
>
>   
>
>   
>
>  So, in this case I’m discharging over 200 gpm due to the number of 
> sprinklers in the area.    Based on this I shouldn’t need to add any 
> additional flow, correct?
>
>   
>
>     
>
>   
>
>     
>
>   
>
>  Thank you,
>
>   
>
>     
>
>   
>
>  Bob Knight, CET III
>
>   
>
>  Fire by Knight, LLC
>
>   
>
>  208-318-3057
>
>   
>
>     
>
>   
>
>  From:    Sprinklerforum 
> [mailto:[email protected]]  On Behalf Of  Shawn 
> Foor via Sprinklerforum
>   Sent:  Tuesday, June 16, 2020 4:23 PM
>   To:   [email protected] (mailto:[email protected]); sprinklerforum
>   Cc:  Shawn Foor
>   Subject:  Re: Floor area less than required
>
>   
>
>   
>
>   
>   
>
> That is the way I read it as well. You would have to add the additional 6 GPM.
>
>   
>   
>
>   
>
>   
>   
>   
>
> On Tue, Jun 16, 2020 at 5:03 PM Bob Knight via Sprinklerforum  
> <[email protected] 
> (mailto:[email protected])>  wrote:
>
>   
>   
> >   
> >   
> >   
> >
> > NFPA 13, 2016 ed. States:
> >
> >   
> >
> >  23.4.4.2.5      Where the total design discharge from these oper-
> >
> >   
> >
> > ating sprinklers is less than the minimum required discharge
> >
> >   
> >
> > determined by multiplying the required design density times
> >
> >   
> >
> > the required minimum design area, an additional flow shall be
> >
> >   
> >
> > added at the point of connection of the branch line to the
> >
> >   
> >
> > cross main furthest from the source to increase the overall
> >
> >   
> >
> > demand, not including hose stream allowance, to the mini-
> >
> >   
> >
> > mum required discharge.
> >
> >   
> >
> >   
> >
> >   
> >
> > This is kinda gray to me.    Does it mean that if I have a light hazard 
> > area that is only 884 sf (offices in a shop)
> >
> >   
> >
> > and the area modifier being applied will allow for a 900 sf area, then I 
> > would need a minimum discharge of 90 gpm over the entire area?
> >
> >   
> >
> > Then, if my calculations bare out 92 gpm nothing else needs done, but if 
> > they came out to 84 gpm an additional flow of 6 gpm would need to be added?
> >
> >   
> >
> >   
> >
> >   
> >
> > Sorry about the run on sentences, just confused.
> >
> >   
> >
> >   
> >
> >   
> >
> >   
> >
> >   
> >
> > Thank you,
> >
> >   
> >
> >   
> >
> >   
> >
> > Bob Knight, CET III
> >
> >   
> >
> > Fire by Knight, LLC
> >
> >   
> >
> >  208-318-3057
> >
> >   
> >
> >
> >
> >   
> >
> >   
> >
> >   
> >   
> >   
> >
> >  _______________________________________________
> >  Sprinklerforum mailing list
> >   [email protected] 
> > (mailto:[email protected])
> >   
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >  
> > (https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwMFaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=_2ppVlQRx7Fb57SSZ9NkK5o7rXDrqJ5TJ7l_rnRCOms&s=ehlEtH7Yni3MIGcXuqxP2PJVlM6NhOL93jbj5WooRyk&e=)
> >
> >   
>   
>   
>
>
>
>
>   
>   
>
>   
>
>   
>   
>
> --
>
>   
>   
>   
>   
>   
>   
>   
>   
>   
>
> Shawn Foor, SET
>
>   
>   
>   
>
>   
>
>   
>   
>   
>
> FOOR DESIGN, LLC
>
>   
>   
>   
>
> 10208 E 98TH ST
>
>   
>   
>   
>
> TULSA, OK 74133
>
>   
>   
>   
>
> P:918-237-1400
>
>   
>   
>   
>   
>   
>   
>   
>   
>   
>  _______________________________________________ Sprinklerforum mailing list 
> [email protected] 
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>   
  
  
     
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
  • Floor area less th... Bob Knight via Sprinklerforum
    • Re: Floor are... Shawn Foor via Sprinklerforum
      • RE: Floor... Bob Knight via Sprinklerforum
        • RE: [... Kyle.Montgomery via Sprinklerforum
          • R... Bob Knight via Sprinklerforum
            • ... Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
              • ... Bob Knight via Sprinklerforum
                • ... Fpdcdesign via Sprinklerforum
                • ... Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
                • ... Bob Knight via Sprinklerforum
                • ... Jussef Liban - GRUPO 3S via Sprinklerforum
                • ... Dennis Wilson via Sprinklerforum
                • ... Hinson, Ryan via Sprinklerforum
                • ... Ron Greenman via Sprinklerforum
                • ... Rod DiBona via Sprinklerforum
                • ... BRUCE VERHEI via Sprinklerforum
            • ... Mike B Morey via Sprinklerforum

Reply via email to