Here is my situation: Hotel Rooms that have a 3'-6" x 2'-6" Non-Combustible 
Concealed space that has a heat pump
unit inside this space. There is not a door into this space only a discharge 
grill that can be removed by the maintenance
staff to get access to service these units.

The local AHJ says that I have to install a sprinkler head to protect this 
space.
The way I interpret NFPA-13 2013 paragraph 8.15.1.2 and 8.15.1.2.2 it does not 
require a sprinkler head in this space.

HELP

Thanks,

Mike