Playing the devil's advocate here, one could argue that the presence of an 
electrically energized air handler negates the part stating "minimal 
combustible loading", that this is actually a mechanical closet not just a 
"concealed space".



Craig Prahl | Jacobs | Group Lead/SME - Fire Protection | 864.676.5252 | 
[email protected] | www.jacobs.com
1041 East Butler Road   Greenville, South Carolina  29606

-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Mike Hairfield via Sprinklerforum
Sent: Thursday, September 10, 2020 1:59 PM
To: [email protected]
Cc: Mike Hairfield <[email protected]>
Subject: [EXTERNAL] Non-Combustible Concealed Space

Here is my situation: Hotel Rooms that have a 3'-6" x 2'-6" Non-Combustible 
Concealed space that has a heat pump unit inside this space. There is not a 
door into this space only a discharge grill that can be removed by the 
maintenance staff to get access to service these units.

The local AHJ says that I have to install a sprinkler head to protect this 
space.
The way I interpret NFPA-13 2013 paragraph 8.15.1.2 and 8.15.1.2.2 it does not 
require a sprinkler head in this space.

HELP

Thanks,

Mike
_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!Vt4rog4BsnH-n57PAPI6zTBxxXnnD4AnQTGFUO0tjw2oFZmauhMmuDeFlR_RtVoASg$

________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to