You can have a 13R system on the 2nd floor and a 13 system on the 1st floor
if they are separated by a 3 hr rated separation. Otherwise, it would have
to be 13 throughout.

On Thu, Sep 17, 2020 at 12:14 PM Thomas Reinhardt via Sprinklerforum <
[email protected]> wrote:

> Hi everyone .Thanks for taking my question. I have a old commercial
> building in town with a store front only two stories. The owner would like
> to convert the second floor to apartment(R-2). We currently use the IFC
> where section 903.2.8 relates that yes sprinklers shall be installed. My
> question is then doesn't the entire building including the apartments shall
> have a NFPA 13 system instead of just a 13R system on the second floor?
>
> _______________________________________________
>
> Sprinklerforum mailing list
>
> [email protected]
>
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
> --
Kevin Hall, P.E., MSFPE
Coordinator, Engineering and Technical Services
American Fire Sprinkler Association