This scenario is very common in hotel occupancies. In order to use NFPA 13R in 
the residential portions, there does not need to be a separation if the 
occupancy is accessory and is less than 10% of the floor area (508.2.3).
If it exceeds 10% then proper separation is required by the IBC table 508.4. In 
order to use 13R, there has to be a 2 hour separation.

I agree that this is the architect's responsibility but y'all see the drawings.

P.S.
Don't paste a snip from the IBC or your post will get bounced.......


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Steve Leyton via Sprinklerforum
Sent: Friday, September 18, 2020 11:45 AM
To: 
[email protected]<mailto:[email protected]>
Cc: Steve Leyton 
<[email protected]<mailto:[email protected]>>; Steven Jenkins 
<[email protected]<mailto:[email protected]>>
Subject: RE: Are sprinklers required

As Steven said, there are a couple "ifs" in the code analysis and the biggest 
one is whether the code official will allow the use of 13R. NFPA 13R doesn't 
give prescriptive guidance but informs in A.1.1 that there may be special rules 
that restrict the use of 13R in mixed occupancies and that the user of the 
standard should:

"Refer to the adopted building code to determine whether such restrictions are 
applicable." This throws to the local building official. My experience in just 
about every (California) jurisdiction has been that a two-headed design is only 
allowed if there is a BUILDING separation between R and B or M occupancies. 
Some allow an occupancy separation between R and S-2 (parking) because if the 
principal use group is R, then parking is accessory to the R can be protected 
per 13 as specifically allowed in 13R. Podium buildings with R over other 
groups generally require a 3 hour horizontal assembly with all utilities and 
stairs shafted with 2-hour fire resistance to even consider the split design 
and in many jurisdictions you have to upgrade to 13 to get additional stories 
of Type 5 anyway. And there are area limits per floor when using a 13R that may 
also restrict its use; you can't just count stories or weigh building 
separations. The charging references are in the allowable hei
ght and area tables of Chapter 5.


Steve Leyton



-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Steven Jenkins via Sprinklerforum
Sent: Friday, September 18, 2020 7:43 AM
To: 
[email protected]<mailto:[email protected]>
Cc: Steven Jenkins <[email protected]<mailto:[email protected]>>
Subject: RE: Are sprinklers required

As seen in the 2015 IFC Commentary to section 903.3.1.2

"... A common question is whether a mixed occupancy building which contains a 
Group R occupancy could still use NFPA 13R for the design. If one of the 
mixed-use occupancies would require a sprinkler system throughout the building 
in accordance with NFPA 13, then a 13R system would not be allowed. If, 
however, the only reason a sprinkler system is being installed is because there 
is a Group R fire area, then a NFPA 13R system would be an appropriate design 
choice.
The areas that are not classified as Group R would require protection in 
accordance with NFPA 13.
It must be noted that although the building would be considered sprinklered 
throughout in accordance with NFPA 13R, not all of the code sprinkler 
alternatives could be applied. Any alternative that requires the installation 
of an NFPA 13 system would not be applicable if a portion of the building 
utilizes an NFPA 13R system...."

Hope this helps,

SJ

-----Original Message-----
From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 On Behalf Of Nick Maneen via Sprinklerforum
Sent: Thursday, September 17, 2020 12:22 PM
To: 
[email protected]<mailto:[email protected]>
Cc: Nick Maneen <[email protected]<mailto:[email protected]>>; Thomas 
Reinhardt <[email protected]<mailto:[email protected]>>
Subject: Re: Are sprinklers required

*** SCDLLR NOTICE ***
* This email is from an external email address. Please use caution when 
deciding whether to open any attachments or when clicking links.
* Personally Identifiable Information (PII) should not be included in e-mail 
text or attachments. Do not save or transmit PII unencrypted.


This is supposed to be above our pay grade, but yeah. Unless the owner wants to 
go through all the trouble of installing rated building separations that would 
allow a 13R structure to sit on a 13 structure, the entire building is 13.

On Thu, Sep 17, 2020 at 12:14 PM Thomas Reinhardt via Sprinklerforum < 
[email protected]<mailto:[email protected]>>
 wrote:

> Hi everyone .Thanks for taking my question. I have a old commercial
> building in town with a store front only two stories. The owner would
> like to convert the second floor to apartment(R-2). We currently use
> the IFC where section 903.2.8 relates that yes sprinklers shall be
> installed. My question is then doesn't the entire building including
> the apartments shall have a NFPA 13 system instead of just a 13R system on 
> the second floor?
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]<mailto:[email protected]>
>
> https://linkprotect.cudasvc.com/url?a=http%3a%2f%2flists.firesprinkler<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2flists.firesprinkler>
> .org%2flistinfo.cgi%2fsprinklerforum-firesprinkler.org&c=E,1,qT-YuUbO_
> l8UbGHbFmTFHwUYkwB-yQ0GKFqEUcMJeEpOKg5NKb6dXvrRFOXcWP7gmkxOEj1iKKcM5Ot
> -ENcUpxjcT8mkjM01v26ylD57QjKDMO5UTevb&typo=1
>


--

Nick Maneen

Estimator

409 W Central Ave

Asheboro, NC 27203

P 336-625-2304

F 336-625-4649

C 704-791-7789
_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
https://linkprotect.cudasvc.com/url?a=http%3a%2f%2flists.firesprinkler.org%2flistinfo.cgi%2fsprinklerforum-firesprinkler.org&c=E,1,KcvmbQpA2WHkRp6q1fFc-t2e8aO3yibFmiIBkMs4p5O1kN5yrgMONJddlTtI_yEvxcbX_yGOAGp2VRK5JR4e8eiT2o7uuqjaykAoEw4BCmlZTXckjH_x&typo=1<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2flists.firesprinkler.org%2flistinfo.cgi%2fsprinklerforum-firesprinkler.org&c=E,1,KcvmbQpA2WHkRp6q1fFc-t2e8aO3yibFmiIBkMs4p5O1kN5yrgMONJddlTtI_yEvxcbX_yGOAGp2VRK5JR4e8eiT2o7uuqjaykAoEw4BCmlZTXckjH_x&typo=1>
_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org<http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org>
_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org<http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to