This is supposed to be above our pay grade, but yeah.  Unless the owner
wants to go through all the trouble of installing rated building
separations that would allow a 13R structure to sit on a 13 structure, the
entire building is 13.

On Thu, Sep 17, 2020 at 12:14 PM Thomas Reinhardt via Sprinklerforum <
[email protected]> wrote:

> Hi everyone .Thanks for taking my question. I have a old commercial
> building in town with a store front only two stories. The owner would like
> to convert the second floor to apartment(R-2). We currently use the IFC
> where section 903.2.8 relates that yes sprinklers shall be installed. My
> question is then doesn't the entire building including the apartments shall
> have a NFPA 13 system instead of just a 13R system on the second floor?