Does the space meet the requirements of "Noncombustible and limited-combustible 
concealed spaces with limited access"? .... if so, should it be sprinkled?

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Skyler Bilbo via Sprinklerforum
Sent: Friday, February 12, 2021 7:21 AM
To: [email protected]
Cc: Skyler Bilbo <[email protected]>
Subject: Re: Bathroom Chase

There is a section that talks about only going back 1.2 times the square root 
of the remote area beyond the ceiling. NFPA 13, 2013 edition, Section 8.15.23.



Skyler Bilbo

On Fri, Feb 12, 2021 at 7:25 AM Brian Harris via Sprinklerforum < 
[email protected]> wrote:

> There's a chase between (2) bathrooms that has an access door which I 
> assume is for maintenance. The drywall stops 6" above ceiling, 
> basically making the entire structure above the ceiling "open". I 
> can't imagine we would need to provide protection at the deck throughout the 
> whole area.
> Seems like I remember something about only needing to protect the deck 
> within a given area?
>
> Brian Harris, CET
> BVS Systems Inc.
> bvssytemsinc.com
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to