At first I thought this was Skyler and I couldn't figure out why he was 
disagreeing with me when I was agreeing with him. 

So then, Cecil, are you of the opinion that the entire area above the ceiling 
would need sprinklers? That doesn't make sense at all. We're essentially 
talking about a mechanical closet with no ceiling; that has to be less 
concerning than the back of house high-piled storage area at a grocery store.

-Kyle M

-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Sprinkler Academy - C Bilbo via Sprinklerforum
Sent: Friday, February 12, 2021 1:06 PM
To: [email protected]
Cc: Sprinkler Academy - C Bilbo <[email protected]>
Subject: [EXTERNAL] Re: Bathroom Chase

While I think the logic path you follow for covering half a remote area one 
direction and then another makes some sense, the Committee was not willing to 
consider a two-sided scenario.  The rule was written such that the area above 
the ceiling is only exposed on one side.  This way, going  two or three 
sprinklers deep would prevent the fire from jumping the wall.  The committee 
would not consider additional measures.   The committee discussed the back of a 
grocery store as the base example in their debates.  Often the back wall that 
separates the storage from the sales floor does not go all the way to the 
ceiling.  This was a remedy to not have to install sprinklers throughout the 
otherwise non-combustible, nearly-concealed space above the grocery store 
ceiling.



It should be recognized that the above is my opinion as a member of the NFPA 13 
Committee, and has not been processed as a formal interpretation in accordance 
with the NFPA Regulations Governing Committee Projects and should therefore not 
be considered, nor relied upon, as the official position of the the NFPA, nor 
any of their technical committees.


Sincerely,


Cecil Bilbo
Academy of Fire Sprinkler Technology
Champaign, IL
217.607.0325
https://urldefense.proofpoint.com/v2/url?u=http-3A__www.sprinkleracademy.com&d=DwICAg&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=jC3qHHMvgwCRbErwQQ7RQnCkuh8NtYfpEDpz84KzNVs&s=iR8ULn5L6U6R6y-RgJQkjF7nClm59agtYo7p94AATWs&e=
 
<https://urldefense.proofpoint.com/v2/url?u=http-3A__www.sprinkleracademy.com&d=DwICAg&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=jC3qHHMvgwCRbErwQQ7RQnCkuh8NtYfpEDpz84KzNVs&s=iR8ULn5L6U6R6y-RgJQkjF7nClm59agtYo7p94AATWs&e=
 > [email protected]<mailto:[email protected]>
??
OUR STUDENTS SAVE LIVES!!


________________________________
From: Sprinklerforum <[email protected]> on behalf 
of Kyle.Montgomery via Sprinklerforum <[email protected]>
Sent: Friday, February 12, 2021 10:29 AM
To: [email protected] 
<[email protected]>
Cc: Kyle.Montgomery <[email protected]>; Brian Harris 
<[email protected]>
Subject: RE: Bathroom Chase

Brian,

I agree with Skyler here. The picture may not look like what you're doing, but 
the book would be hard to carry if there were a figure representing every 
scenario. The intent seems to apply though: You've got a space that is 
sprinklered only because it is open to an adjacent sprinklered space.

I would correct Skyler and say that you only need to extend 0.6 times the 
square root of the remote area, but since you'll have to do that in all 
directions, then it ends up being about 1.2 total.

I would also agree with JD, Nick, and others in questioning whether the area 
needs to have sprinklers at all. But I've seen that interpreted both ways by an 
AHJ.

-Kyle M

-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Brian Harris via Sprinklerforum
Sent: Friday, February 12, 2021 7:53 AM
To: [email protected]
Cc: Brian Harris <[email protected]>
Subject: [EXTERNAL] RE: Bathroom Chase

Skyler-
Thank you. It doesn't look like the example shown in A.8.15.23.3 is the same 
situation I'm running in to.

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com

-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Skyler Bilbo via Sprinklerforum
Sent: Friday, February 12, 2021 9:21 AM
To: [email protected]
Cc: Skyler Bilbo <[email protected]>
Subject: Re: Bathroom Chase

There is a section that talks about only going back 1.2 times the square root 
of the remote area beyond the ceiling. NFPA 13, 2013 edition, Section 8.15.23.



Skyler Bilbo

On Fri, Feb 12, 2021 at 7:25 AM Brian Harris via Sprinklerforum < 
[email protected]> wrote:

> There's a chase between (2) bathrooms that has an access door which I 
> assume is for maintenance. The drywall stops 6" above ceiling, 
> basically making the entire structure above the ceiling "open". I 
> can't imagine we would need to provide protection at the deck throughout the 
> whole area.
> Seems like I remember something about only needing to protect the deck 
> within a given area?
>
> Brian Harris, CET
> BVS Systems Inc.
> bvssytemsinc.com
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkle
> r.org_listinfo.cgi_sprinklerforum-2Dfiresprinkl&d=DwICAg&c=wn3mZQLIuIn
> h2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=G8nBoayLpp
> OEKnsHYV_cnN1XzYYpUKF_Yd4I-drhqSY&s=ZDjvdpiVD244i6ELZm22TPaWz75M8tgfJk
> USdh4OLvQ&e=
> er.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwICAg&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=G8nBoayLppOEKnsHYV_cnN1XzYYpUKF_Yd4I-drhqSY&s=tLVPgHHbvBd2rFhQL9w_SBYxNGVUuMkw5c1_pau5rIg&e=
_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwICAg&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=G8nBoayLppOEKnsHYV_cnN1XzYYpUKF_Yd4I-drhqSY&s=tLVPgHHbvBd2rFhQL9w_SBYxNGVUuMkw5c1_pau5rIg&e=
_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwICAg&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=jC3qHHMvgwCRbErwQQ7RQnCkuh8NtYfpEDpz84KzNVs&s=KurY0NhnL4dowsHNaLqeZK_29GK2IemKZr5ouKRjr5Y&e=
_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwICAg&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=jC3qHHMvgwCRbErwQQ7RQnCkuh8NtYfpEDpz84KzNVs&s=KurY0NhnL4dowsHNaLqeZK_29GK2IemKZr5ouKRjr5Y&e=
 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to