If you need a table showing the weight of the water filled pipe then we have
an Excel sheet that is fillable to determine the weights. We often fill this
out and send to the structural engineer.


Anthony Carrizosa 
Project Manager | Fire Protection 
7855 S 206th St Kent, WA 98032
Cell: 206-679-5283 | Office: 253-872-7222 


https://archerconstruction.com


-----Original Message-----
From: AKS-Gmail-IMAP <[email protected]> 
Sent: Tuesday, February 16, 2021 4:15 PM
To: [email protected]
Subject: Re: MORE ACTIVITY WEIGHING IN

5 lbs/sf collateral load is likely the low bid metal building design. This
loading is intended to include ALL the MEPF and Arch. loads on the
structure. The sprinkler contribution to the 5 lbs/sf is maybe 1.5 lbs/sf.
This loading gets used for sizing the main structural elements. Depending on
the piping layout, sizes, pipe spacing and max hanger spacing the low bid
design purlins might be undersized for some systems and max. hanger spacing.

Note, some metal buildings are specified and bid out prior to the building
MEPF and Arch. loading being determined. Then you have situations where
young people without adequate supervision are running the metal building
software design programs. They may not know how lightweight the design is.
This might give you some context as what is going on. For sure the
collateral numbers are average loads over the entire roof area. The loads
cannot account for where there might be a large main and that is just for
fire protection. The loading does not size for other concentrated loads like
HVAC equipment. If there is seismic involved, the structure would not
necessarily handle system bracing loads at locations where NFPA 13 dictates.

> On Feb 16, 2021, at 1:34 PM, Matt Grise via Sprinklerforum
<[email protected]> wrote:
> 
> When I have looked at it (usually for pre-engineered metal buildings)- the
lbs/sf is just the weight of the water-filled pipe divided by the are it
'covers'. Similar to the coverage of a sprinkler head. 
> 
> Each structural member then has an allowable point-load formula based on
how the connections are spaced and how much load it can handle.
> 
> Most of the PEMB designs I come across have a 5 lbs/ft "collateral load"
design. We have never had a sprinkler system exceed that.
> 
> Matt
> 
> -----Original Message-----
> From: Sprinklerforum <[email protected]> 
> On Behalf Of Vince Sabolik via Sprinklerforum
> Sent: Tuesday, February 16, 2021 1:23 PM
> To: Travis Mack via Sprinklerforum 
> <[email protected]>
> Cc: Vince Sabolik <[email protected]>
> Subject: Re: MORE ACTIVITY WEIGHING IN
> 
> Offices.
> 
> I'm looking for a table that an architect or engineer would use to figure
roof loading.
> I don't think they're that detailed.
> 
> 
> On 2/16/2021 2:17 PM, Travis Mack via Sprinklerforum wrote:
>> What is a typical system?  Protecting flammable liquids will be a lot
more than an office building.
>> 
>> Travis Mack, CFPS, CWBSP, RME-G, COC, SET Engineering Manager MFP 
>> Design
>> 3356 E Vallejo Ct
>> Gilbert, AZ 85298
>> 480-505-9271 ext. 700 C: 480-272-2471 
>> mailto:[email protected]
>> https://linkprotect.cudasvc.com/url?a=https%3a%2f%2fwww.mfpdesign.com
>> &c=E,1,LWPOkuQfKyi4ROGqKcnbYQjv2Y6W-GC52ALx7gZ_ozT4hvUsEfdfMFU1zDo69t
>> l0F8jhudt85K7GliMneCJSs-0mA2XIq4vv7cNfCaG8A7EfttrZ5KDqiwaXUQ,,&typo=1
>> 
>> Send large files to us via: 
>> https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.
>> hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108
>> d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C6363790166773
>> 42180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved
>> =0
>> 
>> From: Sprinklerforum <[email protected]> 
>> On Behalf Of Vince Sabolik via Sprinklerforum
>> Sent: Tuesday, February 16, 2021 12:16 PM
>> To: [email protected]
>> Cc: Vince Sabolik <[email protected]>
>> Subject: MORE ACTIVITY WEIGHING IN
>> 
>> Hello forum -
>> 
>> Does anyone have tables of how much weight per square foot a typical 
>> sprinkler system adds to a building?
>> 
>> thanks, Vince
> 
> 
> --
> 
> 11351 Pearl Road /  Suite 101
> Strongsville, Ohio 44136
> Phone 440 238-4800 Fax 440 238-4876Cell 440 724-7601
> 
> /
> Vince Sabolik /
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> https://linkprotect.cudasvc.com/url?a=http%3a%2f%2flists.firesprinkler
> .org%2flistinfo.cgi%2fsprinklerforum-firesprinkler.org&c=E,1,NPrDsZFoJ
> HdeIk_5-R2AUIsPqjilTuTkcD587y6E7Dx0b5oQNOxLX8krqo5dLEReyOSkeIodEc43NE1
> QVoQjLFnVHztKtqX9EhY213_EzJPT69DC&typo=1
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to