I have a small dealership renovation we are designing now.  An issue has
come up with the calculations we are having a difficult time solving, and I
wanted to pick the forums collective brain on it.
Looking at the existing system, it appears the original install contractor
utilized the QR reduction in the showroom to reduce the design area.  The
renovation calls for increasing the 130 sqft vestibule ceiling height to
26' from 17'.  This essentially eliminates our ability to apply the QR
reduction, and defaults our remote area back to 1500 sqft.  Unfortunately,
we don't have the water to make this remote area work anymore.  Is anyone
aware of a way to keep the reduced design area?  I have been racking my
brain on this, trying to eliminate the need for a pump.
Thanks again forum...
Jamie Seidl