Nope, the existing system was already 11.2k ECOH spaced at 14'x14' with an
ehp of 7.2.  They milked it...
Thanks John.

On Thu, Apr 29, 2021 at 9:52 AM John Denhardt via Sprinklerforum <
[email protected]> wrote:

> No other option.  1,500 Sq.Ft. minimum remote area.
>
> Any chance adjusting K factors of the sprinklers?
>
> *The above is my opinion and has not been processed as a formal
> interpretation in accordance with the NFPA Regulations Governing Committee
> Projects. This is provided with the understanding that the AFSA assumes no
> liability for this opinion or actions taken on it and they are not to be
> considered the official position of the **AFSA, and/or NFPA or its
> technical committees.**AFSA cannot provide design or consulting engineering
> services, and this opinion should therefore not be considered, nor relied
> upon, as such.*
>
> Thanks,
> John
>
> John August Denhardt, PE
> *Vice President, Engineering and Technical Services*
>
> *American Fire Sprinkler Association*
> m: p: 301-343-1457
> 214-349-5965 ext 121
> w: firesprinkler.org
> <https://www.facebook.com/firesprinkler.org/>
> <https://twitter.com/afsa/status/1039528345367732224>
> <
> https://www.linkedin.com/company/american-fire-sprinkler-association-afsa-/
> >
>    <https://www.instagram.com/firesprinklerorg/>
>
> *Our members are at the heart of everything we do*
>
>
> *Enter your apprentices to win a trip to San Antonio!*
>
> Deadline to enter to compete in the 28th Annual National Apprentice
> Competition is April 30, 2021. Don't miss this opportunity to be recognized
> for your training efforts! *It’s free to enter online at *
> https://www.firesprinkler.org/competition
>
>
> On Thu, Apr 29, 2021 at 9:48 AM Jamie Seidl via Sprinklerforum <
> [email protected]> wrote:
>
> > I have a small dealership renovation we are designing now.  An issue has
> > come up with the calculations we are having a difficult time solving,
> and I
> > wanted to pick the forums collective brain on it.
> > Looking at the existing system, it appears the original install
> contractor
> > utilized the QR reduction in the showroom to reduce the design area.  The
> > renovation calls for increasing the 130 sqft vestibule ceiling height to
> > 26' from 17'.  This essentially eliminates our ability to apply the QR
> > reduction, and defaults our remote area back to 1500 sqft.
> Unfortunately,
> > we don't have the water to make this remote area work anymore.  Is anyone
> > aware of a way to keep the reduced design area?  I have been racking my
> > brain on this, trying to eliminate the need for a pump.
> > Thanks again forum...
> > Jamie Seidl
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to