Mike,

I'm not sure which edition of the standard governs this project, however:
from the 2016:
8.15.1.2.1 concealed spaces of non- or limited combustible construction require no sprinklers 8.15.1.2.2 concealed spaces of non- or limited combustible construction with limited access, and no occupancy, or storage of combustibles require no sprinklers.

Those same sections are unmodified in the '19 edition, in 9.2.1.1 and 9.2.1.2.

hope that helps,
*Ken Wagoner, SET
*Parsley Consulting*
*350 West 9th Avenue, Suite 206
*Escondido, California 92025
*****Phone 760-745-6181*
Visit the website <http://www.parsleyconsulting.com/> *****


**
On 5/11/2021 12:38 PM, Mike Hairfield via Sprinklerforum wrote:
Got a project where there is a walkable ceiling with a non-combustible 
interstitial space above.

FM Global did not require sprinkler protection in this space.

The local AHJ is saying that it needs to be protected with sprinklers.

Where in NFPA-13 can I find where it doesn't require protection.

Thanks,

Mike