What's the occupancy classification of the occupied space below?

Next question, what is the interstitial space being used for?



Craig Prahl | Jacobs | Group Lead/SME - Fire Protection | 
[email protected] | www.jacobs.com
1041 East Butler Road   Greenville, South Carolina  29606
CONTACT BY: email or MS TEAMS

-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Mike Hairfield via Sprinklerforum
Sent: Tuesday, May 11, 2021 3:39 PM
To: Sprinkler Forum <[email protected]>
Cc: Mike Hairfield <[email protected]>
Subject: [EXTERNAL] Interstitial Space

Got a project where there is a walkable ceiling with a non-combustible 
interstitial space above.

FM Global did not require sprinkler protection in this space.

The local AHJ is saying that it needs to be protected with sprinklers.

Where in NFPA-13 can I find where it doesn't require protection.

Thanks,

Mike
_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!UID9wG7g5YhwDol7uTCN9CuJrbbCMG5ZpCOZJDBi-AxJ9_5RjLPtCPnwQzSFBnZXPA$

________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to