Way back-in-the-day, when NFPA 13 would fit in a back pocket, there was a Formal Interpretation 80-29(A) that addressed interstitial spaces. It remained in play until at least the 1999 edition, there is a copy in the '99 Handbook. I never saw it "withdrawn", but it was probably dropped from reference when NFPA 13 added text for concealed spaces not requiring sprinkler protection, because it doesn't seem to be in the '02 Handbook.
Anyway, here is what that old FI said in the '99 Handbook: Formal Interpretation 80-29(A) Reference 5-1.1, 5-13.1.3 Background: Construction - Structural steel frame with concrete floors. The floor-to-floor height is approximately 15½ feet. Approximately 9 feet above each floor, a gypsum deck has been poured to form an "interstitial space." Non-combustible ductwork, plumbing, electrical conduit, sprinkler piping and open cable trays run in the interstitial space. Access to the space is by five stairways, with access doors each being approximately 3 feet by 3 feet. Question: Is it the intent of 5-1.1 of NFPA 13 that sprinkler protection of the interstitial space described above be provided to consider the building completely protected by automatic sprinklers? Answer: No. The space described is essentially non-combustible with no occupancy and no combustible services [with the possible exception of the cable trays which could be protected in accordance with 5-5.1.3 if necessary] and so could be treated as a non-combustible concealed space. Use of the space for storage or the introduction of combustibles would require provision of sprinklers to maintain classification as completely protected by automatic sprinklers. Issue Edition: 1980 Reference: 3-10.3, 4.1 Date: October 1982 Please note there is a typo in that FI, because there is no 5-5.1.3 in NFPA 13-1999, and 5-13.1.3 does not seem to be applicable either. I think that reference in the answer should have been to 5-13.1.4 (b), which is the text that was referenced (as 4.4.4.4 (b)) in previous Handbooks in my library. I hope that you find this helpful, Larry Keeping -----Original Message----- From: Sprinklerforum <[email protected]> On Behalf Of Ken Wagoner via Sprinklerforum Sent: May 11, 2021 3:51 PM To: [email protected] Cc: Ken Wagoner <[email protected]>; Mike Hairfield <[email protected]> Subject: Re: Interstitial Space Warning! This email came from outside your company. Mike, I'm not sure which edition of the standard governs this project, however: from the 2016: 8.15.1.2.1 concealed spaces of non- or limited combustible construction require no sprinklers 8.15.1.2.2 concealed spaces of non- or limited combustible construction with limited access, and no occupancy, or storage of combustibles require no sprinklers. Those same sections are unmodified in the '19 edition, in 9.2.1.1 and 9.2.1.2. hope that helps, *Ken Wagoner, SET *Parsley Consulting* *350 West 9th Avenue, Suite 206 *Escondido, California 92025 *****Phone 760-745-6181* Visit the website <http://www.parsleyconsulting.com/> ***** ** On 5/11/2021 12:38 PM, Mike Hairfield via Sprinklerforum wrote: > Got a project where there is a walkable ceiling with a non-combustible > interstitial space above. > > FM Global did not require sprinkler protection in this space. > > The local AHJ is saying that it needs to be protected with sprinklers. > > Where in NFPA-13 can I find where it doesn't require protection. > > Thanks, > > Mike > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl > er.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
