We have a wood framed building where the stair shaft is made of wood with
drywall that gives it a 3 hour fire rating. The stairs are steel and
concrete.

I have been asked if we need to provide sprinkler heads at each level or
just at the top and below the lowest landing. We are currently in the 2013
edition of NFPA 13.

I am a bit confused on the wording in Section 8.15.3.1 where they reference
sprinklers beneath all stairways of combustible construction. Section
8.15.3.2.1 references non combustible stair shafts  having non combustible
stairs with non combustible or limited combustible finishes requiring
sprinklers only at the top and under the first accessible landing. I would
be interested in the forum's opinion on this.

 

 