Is there any combustible construction within the stairway?
 
 
 
 Todd G Williams, PE 
Fire Protection Design/Consulting
 
Stonington, CT
 
860-535-2080 (tel:860-535-2080)  (ofc)
 
860-554-7054 (tel:860-554-7054)     (fax)
 
860-608-4559 (tel:860-608-4559)  (cell)
 
 
 
 

 
 
>  
> On Jun 24, 2021 at 6:17 AM,  <Bruce Hermanson via Sprinklerforum 
> (mailto:[email protected])>  wrote:
>  
>  
>  
>  We have a wood framed building where the stair shaft is made of wood with 
> drywall that gives it a 3 hour fire rating. The stairs are steel and 
> concrete. I have been asked if we need to provide sprinkler heads at each 
> level or just at the top and below the lowest landing. We are currently in 
> the 2013 edition of NFPA 13. I am a bit confused on the wording in Section 
> 8.15.3.1 where they reference sprinklers beneath all stairways of combustible 
> construction. Section 8.15.3.2.1 references non combustible stair shafts 
> having non combustible stairs with non combustible or limited combustible 
> finishes requiring sprinklers only at the top and under the first accessible 
> landing. I would be interested in the forum's opinion on this. Bruce 