I'm not an expert on this particular section, but to me it's a matter of 
differentiating "stairway" from "stair shaft".  The stairway, imho, is what you 
stand on, and the shaft is what it's in.  If we were to remove the stairs and 
just call this a vertical shaft, would it be a combustible or non-combusible?  
If it was wood framed but covered on the side facing the shaft with sheet rock 
I'm saying it's a non-combustible shaft.  And since it contains a 
non-combustible stairway which doesn't trigger the first section I would move 
on to the second section which to me is applicable as the "shaft" itself is 
non-com.  I would design it with a head at the top and bottom and let someone 
show me why that isn't correct.  The wood framing itself lives in it's own 
combustible concealed space, but that's exempted from protection and the 3k sq 
ft as long as it's a typical wall stud/drywall arrangement.

Mike Morey
CFPS 3229 * NICET S.E.T. 123677
Project Manager * Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive * Fort Wayne, IN * 46825
direct 260.487.7824 /  cell 260.417.0625 /  fax 260.487.7991
email [email protected]



-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Bruce Hermanson via Sprinklerforum
Sent: Thursday, June 24, 2021 6:17 AM
To: [email protected]
Cc: [email protected]
Subject: Sprinklers in stairways

 
BE ADVISED - This email originated outside EMCOR. 
 

We have a wood framed building where the stair shaft is made of wood with 
drywall that gives it a 3 hour fire rating. The stairs are steel and concrete.

I have been asked if we need to provide sprinkler heads at each level or just 
at the top and below the lowest landing. We are currently in the 2013 edition 
of NFPA 13.

I am a bit confused on the wording in Section 
https://urldefense.com/v3/__http://8.15.3.1__;!!FaxH778!OPhfng3N2P1Kg7dYtLr-pb5SM8-vcH6y-gW6XUVgBVbjhBLx1JI9hhhBPjRcvJGm$
  where they reference sprinklers beneath all stairways of combustible 
construction. Section
8.15.3.2.1 references non combustible stair shafts  having non combustible 
stairs with non combustible or limited combustible finishes requiring 
sprinklers only at the top and under the first accessible landing. I would be 
interested in the forum's opinion on this.

 

 

Bruce Hermanson

President TSFP Holdings Inc.

(734) 454-1350

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!FaxH778!OPhfng3N2P1Kg7dYtLr-pb5SM8-vcH6y-gW6XUVgBVbjhBLx1JI9hhhBPlATk0uB$
 

This message is for the named person's use only.  It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission.  If you receive this message in 
error, please  immediately delete it and all copies of it from your system, 
destroy any hard copies of it and notify the sender.  You must not, directly or 
indirectly, use, disclose, distribute, print, or copy any part of this message 
if you are not the intended recipient.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to