I'll be devil's advocate. Pipe scheduled systems don't have limits on drop
lengths and I've seen a few scheduled warehouse systems with 30 to 40 ft.
roof decks with sections of office spacing below at 10 ft. with pendents
feeding them. So if you can do it per the pipe scheduled method you should
be able to do it with a shorter 6 ft. flex hose with the same equivalent
feet that you might find in a hard piped system.

JH

On Mon, Aug 2, 2021 at 11:07 AM Sean Lockyer via Sprinklerforum <
[email protected]> wrote:

> Can flexible hose head connectors (I.E. - "Flexheads") be used on a pipe
> scheduled system ? Since calculations were not performed due to it being a
> scheduled system, the friction loss would be superfluous, correct ? Any
> help would be greatly appreciated.
>
> Thanks
> Sean Lockyer
> AIT Life Safety
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>