For the jockey piping - I wonder if the engineer meant to say that you could 
pressurize the portion of the piping between the backflow preventer and the 
fire pump with the jockey pump. Maybe have an additional check valve after the 
BFP, but before the pump. Then when the pump first activates, there would be a 
certain amount of water present in the impeller with positive pressure to 'get 
things moving'. It seems like an interesting idea, but I don't know if it would 
actually help or not (I have never tried/heard of anything similar).

I don't suppose the school has the budget for a break tank?

Matt 


-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Skyler Bilbo via Sprinklerforum
Sent: Wednesday, August 25, 2021 8:09 PM
To: [email protected]
Cc: Skyler Bilbo <[email protected]>
Subject: Re: Fire Pump Backflow

I never had this problem before, but it looks like a Deringer 20 backflow has 
lower opening pressures.  You may also consider something like several smaller 
Watts 2000B-FP in parallel, depending on the flows you need.

I don't think piping the jockey differently would help, but let me know if you 
get a good explanation on that one.



Skyler Bilbo

1700 S. Raney Street
Effingham, IL 62401
217-819-6404 Direct
217-347-7315 Fax

[email protected]
https://linkprotect.cudasvc.com/url?a=https%3a%2f%2fwww.wenteplumbing.com&c=E,1,h2okMwFsjIDCQhmya-Kx06mz3tFZupKU7w05xn3QZHOB0--IU_VdrTM1lonijtBzoi9cjzdvmsUyOm6BPXv89zxI0Sy1rmwwqd6UERe8cHOeY704KFPtZmmvJLg,&typo=1


On Wed, Aug 25, 2021 at 6:19 PM Jamie Seidl via Sprinklerforum < 
[email protected]> wrote:

> What is your site elevation AMSL?  Have you tried to operate the pump yet?
> While we typically don't run pumps below 0 psi, it can be done by 
> figuring in by also accounting for air pressure.  While not 
> recommended, as long as you are not cavitating the impeller, the system 
> should work.
> I had a similar situation on an alternate water supply (seismic) 
> ground level pool surface that was roughly 1' below the pump inlet. We 
> discussed it with an engineer, and he said we could figure on 
> approximately 14 psi of additional pressure (PSIA) acting on the 
> surface of the pool.  When we tested it, it worked without a hitch.
> Once you pass the opening spring pressure, BFP's typically drop in 
> loss to a point.  PSIA may give you enough pressure to make the system work.
> I've used this principal on subsequent projects where site conditions 
> didn't allow for positive pressure on inlets.
> https://linkprotect.cudasvc.com/url?a=https%3a%2f%2fkimray.com%2ftrain
> ing%2fpsia-vs-psig-whats-difference&c=E,1,1F4X6eSJbL6wWFwR4iXZRTYNAiR7
> HF08Yy5JnLooBVZA57cbQmgLJwq64vjS1eFxGteVWO42Z-0h1HnLUCwn1YZ09gVFjllwZH
> gzhwiVkHoYuomKVSLvcw8,&typo=1
> Jamie Seidl
>
> On Wed, Aug 25, 2021 at 4:25 PM Joe Burtell via Sprinklerforum < 
> [email protected]> wrote:
>
> > Yes, we have pottable water being taken from the same tanks. This is 
> > a rural high school and this is their own water system that feeds 
> > the
> school.
> > So I need the backflow for that reason.
> >
> > Best regards,
> >
> > *Joe Burtell, SET, CFPS*
> >
> > [image: Burtell Fire_Small]
> >
> > Phone | Fax | Mobile| Text *406-204-4653 <++1-406-204-4653>*
> >
> > 116 N. 11th Street | Billings, MT 59101
> >
> > Email: [email protected]
> >
> > Web Site: 
> > https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.burtellfire.c
> > om&c=E,1,pJTgzEU_XFuYlvmpK9o1iCkZypABzB5IoHk4OjCOEBIFUd5Kd7miOas9TZo
> > Q49uebildsyzmQwps1LkQanSB6JH52W2b0TlXfuspQ_4TVeeFMQ,,&typo=1
> >
> > *“**The bitterness of poor quality remains long after the sweetness 
> > of
> low
> > price is forgotten.**”*
> >
> > *NOTICE:*  The information contained in this e-mail transmission is 
> > intended only for use of the individual or entity named above.  This
> e-mail
> > transmission, and any documents, files, previous e-mail 
> > transmissions or other information attached to it, may contain 
> > confidential information
> that
> > is legally privileged.  If you are not the intended recipient of 
> > this e-mail transmission, or the employee or agent responsible for 
> > delivering
> it
> > to the intended recipient, you are hereby notified that any 
> > disclosure, dissemination, distribution, copying or other use of 
> > this transmission or any of the information contained in or attached 
> > to this e-mail is
> strictly
> > prohibited.  If you have received this e-mail transmission in error,
> please
> > immediately notify us by return e-mail transmission and destroy the 
> > original e-mail transmission as well as its attachments without 
> > reading
> or
> > saving it in any manner.  Thank you.
> >
> >
> > On Wed, Aug 25, 2021 at 1:40 PM cliff--- via Sprinklerforum < 
> > [email protected]> wrote:
> >
> > > Hi Joe,
> > >
> > > Why would you need the BFP if you have storage tanks?  Are there 
> > > other systems being fed from the same tanks that would necessitate the 
> > > BFP?
> > >
> > > Cliff Whitfield, SET
> > > President
> > >
> > > Fire Design, Inc.
> > > 940 Summerbrooke Drive
> > > Tallahassee, FL 32312
> > > Ph: 828-284-4772
> > >
> > >
> > >
> > > [email protected]
> > > https://linkprotect.cudasvc.com/url?a=https%3a%2f%2fwww.fire-desig
> > > n.com&c=E,1,3JWvfK1ys9q_zmWNWu7eGNEzfNF_imyTCXsA69Dw5EXEI714QvJqkQ
> > > nD3kMBXZ3FeFh-3R-3PRB7X0VApyBH-zuEmq-ZoxX2abpv4TNZtrNj_XrmneM2&typ
> > > o=1
> > >
> > > -----Original Message-----
> > > From: Sprinklerforum 
> > > <[email protected]>
> On
> > > Behalf Of Joe Burtell via Sprinklerforum
> > > Sent: Wednesday, August 25, 2021 3:33 PM
> > > To: [email protected]
> > > Cc: Joe Burtell <[email protected]>
> > > Subject: Fire Pump Backflow
> > >
> > > I have a situation with a verticle in-line fire pump fed from 
> > > water storage tanks. We have a double check backflow installed 
> > > between the
> > tanks
> > > and the fire pump but we don't have enough pressure to open the
> backflow
> > on
> > > the upstream side between the tank and backflow. I talked with 
> > > Watts
> > about
> > > it. They stated there are no backflows with weaker springs. I only 
> > > have about 7 PSI out of the tanks. Has anyone ran into this 
> > > situation before
> > and
> > > have any suggestions to resolve the issue? The engineer suggested
> piping
> > > the jockey pump before the backflow. Not sure how that would work 
> > > in
> > theory.
> > >
> > > Best regards,
> > >
> > > *Joe Burtell, SET, CFPS*
> > >
> > > [image: Burtell Fire_Small]
> > >
> > > Phone | Fax | Mobile| Text *406-204-4653 <++1-406-204-4653>*
> > >
> > > 116 N. 11th Street | Billings, MT 59101
> > >
> > > Email: [email protected]
> > >
> > > Web Site: 
> > > https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.burtellfire
> > > .com&c=E,1,mIS0DGsb3z0wjTyb83882uSgINqgEFSGqLh18uWfYKCOnl3nwa2TC-0
> > > fcXvhg0j4XSJsuAWqyMpdtzdHuSJ_WxvO3Q7o-hPO8xm9_oxxdjk7&typo=1
> > >
> > > *“**The bitterness of poor quality remains long after the 
> > > sweetness of
> > low
> > > price is forgotten.**”*
> > >
> > > *NOTICE:*  The information contained in this e-mail transmission 
> > > is intended only for use of the individual or entity named above.  
> > > This
> > e-mail
> > > transmission, and any documents, files, previous e-mail 
> > > transmissions
> or
> > > other information attached to it, may contain confidential 
> > > information
> > that
> > > is legally privileged.  If you are not the intended recipient of 
> > > this e-mail transmission, or the employee or agent responsible for
> delivering
> > it
> > > to the intended recipient, you are hereby notified that any 
> > > disclosure, dissemination, distribution, copying or other use of 
> > > this transmission
> or
> > > any of the information contained in or attached to this e-mail is
> > strictly
> > > prohibited.  If you have received this e-mail transmission in 
> > > error,
> > please
> > > immediately notify us by return e-mail transmission and destroy 
> > > the original e-mail transmission as well as its attachments 
> > > without reading
> > or
> > > saving it in any manner.  Thank you.
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > >
> > >
> >
> https://linkprotect.cudasvc.com/url?a=http%3a%2f%2flists.firesprinkler
> .org%2flistinfo.cgi%2fsprinklerforum-firesprinkler.org&c=E,1,4VOnCEl3g
> waEY2VAPtM1iKmbiusGFEm9CpR9Cwc6L6nrc5eFjWIs84u1XWaB78YdnoRAJEoRz6SEcMk
> I1-5Hs-32VS2XHchq1XNaGCEHk-InxSBOP5aFm0Rp2Ag,&typo=1
> > >
> > >
> > > --
> > > This email has been checked for viruses by Avast antivirus software.
> > > https://www.avast.com/antivirus
> > >
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > >
> > >
> >
> https://linkprotect.cudasvc.com/url?a=http%3a%2f%2flists.firesprinkler
> .org%2flistinfo.cgi%2fsprinklerforum-firesprinkler.org&c=E,1,96bV5Oi1D
> 8ruAOPq3axsncbM5yDM_93JaNKDzGo8oiQ7zfv_4ItLiBnvAKk8RzW8ABRK3sW3ppZ-LLx
> NIQStHiBKM415_dLxdfVOUfBQgg,,&typo=1
> > >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> >
> https://linkprotect.cudasvc.com/url?a=http%3a%2f%2flists.firesprinkler
> .org%2flistinfo.cgi%2fsprinklerforum-firesprinkler.org&c=E,1,idZ_gCy9G
> -ItvigFEBvfRhbxdtfohvvex8-mhTd2SErAZv2umPd-IFMEruYmB9Oc4uftaXc5WnHHVC7
> coiIbqSwv2pGhRDFteGjY1ho5L7whM15pBl3uZg,,&typo=1
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> https://linkprotect.cudasvc.com/url?a=http%3a%2f%2flists.firesprinkler
> .org%2flistinfo.cgi%2fsprinklerforum-firesprinkler.org&c=E,1,rmkBt62Bg
> 4EjC7RH56JQsMGVOO_OSY7K9T_lcmqBY9y35srAK0Ulorrd_jJHnaLZFCgNDgBZ7Ypcg5B
> KIriJ42NbWiFR5cxEy41VQL9t&typo=1
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
https://linkprotect.cudasvc.com/url?a=http%3a%2f%2flists.firesprinkler.org%2flistinfo.cgi%2fsprinklerforum-firesprinkler.org&c=E,1,owpJ2vVKG3vmRNCE780smi3mDdQO8j7syKJMQjA-eFq0-CGXRilgPYnoc8i4kGPMVvdkIOnorpN4SKMHhykvE0WDODDyr1lZ7zUY06c5Q3ZTLdlBYv-nORpS&typo=1
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to