Joe,

Is this a real problem or a theoretical problem? What I mean is, are you still 
in the design phase or is it actually installed like this and causing a 
problem? 

I could see there maybe being some trouble initially just getting all the air 
out of the system. Maybe you could use a valved bypass around the backflow just 
to prime everything. Or is there a small backflow preventer with a lower 
opening pressure that you could run in parallel with the larger one? 

But once the system is primed and full of water, that backflow is going to open 
when the pump kicks on for sure. Maybe you have a negative gauge pressure on 
the suction side for a split-second but is that enough to cause a problem with 
the pump? Unlike a pool pump, there is no way for air to enter the system if 
the pump pulls a vacuum, so I think the pump would just pull the backflow open 
and you'd be on your merry way.

If I'm wrong (and there's a pretty good chance of that), I'd appreciate a 
lesson in the physics of how/why?

-Kyle M


-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Prahl, Craig/GVL via Sprinklerforum
Sent: Thursday, August 26, 2021 5:44 AM
To: [email protected]
Cc: Prahl, Craig/GVL <[email protected]>; Matt Grise <[email protected]>
Subject: [EXTERNAL] RE: Fire Pump Backflow

I have doubts that the "engineer" has any clue what a jockey pump does or how 
it works.

So, you'd have a connection on the suction side of the fire pump that typically 
connects back to the discharge side of the pump. Does the engineer think you 
are going to take and route another connection off the discharge of the jockey 
back to the inlet side of the BFP?

Just think about this.

I don't think I've yet seen why this BFP is part of this system?  Is the tank 
dual purpose, potable and fire?

Craig Prahl | Jacobs | Group Lead/SME – Fire Protection | 
[email protected] | 
https://urldefense.proofpoint.com/v2/url?u=http-3A__www.jacobs.com&d=DwIGaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=88jST93e_Oe8-2XMNGySKXvF1erV-mY3sycrFA20UKA&s=yIn1a-3qh8lN41LbJVnadB5QFxk0vddC8nfYTKxTzJI&e=
 
1041 East Butler Road   Greenville, South Carolina  29606
CONTACT BY: email or MS TEAMS



-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Matt Grise via Sprinklerforum
Sent: Thursday, August 26, 2021 7:19 AM
To: [email protected]
Cc: Matt Grise <[email protected]>
Subject: [EXTERNAL] RE: Fire Pump Backflow

For the jockey piping - I wonder if the engineer meant to say that you could 
pressurize the portion of the piping between the backflow preventer and the 
fire pump with the jockey pump. Maybe have an additional check valve after the 
BFP, but before the pump. Then when the pump first activates, there would be a 
certain amount of water present in the impeller with positive pressure to 'get 
things moving'. It seems like an interesting idea, but I don't know if it would 
actually help or not (I have never tried/heard of anything similar).

I don't suppose the school has the budget for a break tank?

Matt


-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Skyler Bilbo via Sprinklerforum
Sent: Wednesday, August 25, 2021 8:09 PM
To: [email protected]
Cc: Skyler Bilbo <[email protected]>
Subject: Re: Fire Pump Backflow

I never had this problem before, but it looks like a Deringer 20 backflow has 
lower opening pressures.  You may also consider something like several smaller 
Watts 2000B-FP in parallel, depending on the flows you need.

I don't think piping the jockey differently would help, but let me know if you 
get a good explanation on that one.



Skyler Bilbo

1700 S. Raney Street
Effingham, IL 62401
217-819-6404 Direct
217-347-7315 Fax

[email protected]
https://urldefense.com/v3/__https://linkprotect.cudasvc.com/url?a=https*3a*2f*2fwww.wenteplumbing.com&c=E,1,h2okMwFsjIDCQhmya-Kx06mz3tFZupKU7w05xn3QZHOB0--IU_VdrTM1lonijtBzoi9cjzdvmsUyOm6BPXv89zxI0Sy1rmwwqd6UERe8cHOeY704KFPtZmmvJLg,&typo=1__;JSUl!!B5cixuoO7ltTeg!TTHVu3P9zPjyVb6NpB9AS2V987_FU3EZOWFLItv8uvHaNSNBZHRy6nVpsyIJdgSJ_g$


On Wed, Aug 25, 2021 at 6:19 PM Jamie Seidl via Sprinklerforum < 
[email protected]> wrote:

> What is your site elevation AMSL?  Have you tried to operate the pump yet?
> While we typically don't run pumps below 0 psi, it can be done by 
> figuring in by also accounting for air pressure.  While not 
> recommended, as long as you are not cavitating the impeller, the system 
> should work.
> I had a similar situation on an alternate water supply (seismic) 
> ground level pool surface that was roughly 1' below the pump inlet. We 
> discussed it with an engineer, and he said we could figure on 
> approximately 14 psi of additional pressure (PSIA) acting on the 
> surface of the pool.  When we tested it, it worked without a hitch.
> Once you pass the opening spring pressure, BFP's typically drop in 
> loss to a point.  PSIA may give you enough pressure to make the system work.
> I've used this principal on subsequent projects where site conditions 
> didn't allow for positive pressure on inlets.
> https://urldefense.com/v3/__https://linkprotect.cudasvc.com/url?a=http
> s*3a*2f*2fkimray.com*2ftrain__;JSUlJQ!!B5cixuoO7ltTeg!TTHVu3P9zPjyVb6N
> pB9AS2V987_FU3EZOWFLItv8uvHaNSNBZHRy6nVpsyJdhKSSuQ$
> ing%2fpsia-vs-psig-whats-difference&c=E,1,1F4X6eSJbL6wWFwR4iXZRTYNAiR7
> HF08Yy5JnLooBVZA57cbQmgLJwq64vjS1eFxGteVWO42Z-0h1HnLUCwn1YZ09gVFjllwZH
> gzhwiVkHoYuomKVSLvcw8,&typo=1
> Jamie Seidl
>
> On Wed, Aug 25, 2021 at 4:25 PM Joe Burtell via Sprinklerforum < 
> [email protected]> wrote:
>
> > Yes, we have pottable water being taken from the same tanks. This is 
> > a rural high school and this is their own water system that feeds 
> > the
> school.
> > So I need the backflow for that reason.
> >
> > Best regards,
> >
> > *Joe Burtell, SET, CFPS*
> >
> > [image: Burtell Fire_Small]
> >
> > Phone | Fax | Mobile| Text *406-204-4653 <++1-406-204-4653>*
> >
> > 116 N. 11th Street | Billings, MT 59101
> >
> > Email: [email protected]
> >
> > Web Site:
> > https://urldefense.com/v3/__https://linkprotect.cudasvc.com/url?a=ht
> > tp*3a*2f*2fwww.burtellfire.c__;JSUl!!B5cixuoO7ltTeg!TTHVu3P9zPjyVb6N
> > pB9AS2V987_FU3EZOWFLItv8uvHaNSNBZHRy6nVpsyJKYIzM1Q$
> > om&c=E,1,pJTgzEU_XFuYlvmpK9o1iCkZypABzB5IoHk4OjCOEBIFUd5Kd7miOas9TZo
> > Q49uebildsyzmQwps1LkQanSB6JH52W2b0TlXfuspQ_4TVeeFMQ,,&typo=1
> >
> > *“**The bitterness of poor quality remains long after the sweetness 
> > of
> low
> > price is forgotten.**”*
> >
> > *NOTICE:*  The information contained in this e-mail transmission is 
> > intended only for use of the individual or entity named above.  This
> e-mail
> > transmission, and any documents, files, previous e-mail 
> > transmissions or other information attached to it, may contain 
> > confidential information
> that
> > is legally privileged.  If you are not the intended recipient of 
> > this e-mail transmission, or the employee or agent responsible for 
> > delivering
> it
> > to the intended recipient, you are hereby notified that any 
> > disclosure, dissemination, distribution, copying or other use of 
> > this transmission or any of the information contained in or attached 
> > to this e-mail is
> strictly
> > prohibited.  If you have received this e-mail transmission in error,
> please
> > immediately notify us by return e-mail transmission and destroy the 
> > original e-mail transmission as well as its attachments without 
> > reading
> or
> > saving it in any manner.  Thank you.
> >
> >
> > On Wed, Aug 25, 2021 at 1:40 PM cliff--- via Sprinklerforum < 
> > [email protected]> wrote:
> >
> > > Hi Joe,
> > >
> > > Why would you need the BFP if you have storage tanks?  Are there 
> > > other systems being fed from the same tanks that would necessitate the 
> > > BFP?
> > >
> > > Cliff Whitfield, SET
> > > President
> > >
> > > Fire Design, Inc.
> > > 940 Summerbrooke Drive
> > > Tallahassee, FL 32312
> > > Ph: 828-284-4772
> > >
> > >
> > >
> > > [email protected]
> > > https://urldefense.com/v3/__https://linkprotect.cudasvc.com/url?a=
> > > https*3a*2f*2fwww.fire-desig__;JSUl!!B5cixuoO7ltTeg!TTHVu3P9zPjyVb
> > > 6NpB9AS2V987_FU3EZOWFLItv8uvHaNSNBZHRy6nVpsyJN9fFlQA$
> > > n.com&c=E,1,3JWvfK1ys9q_zmWNWu7eGNEzfNF_imyTCXsA69Dw5EXEI714QvJqkQ
> > > nD3kMBXZ3FeFh-3R-3PRB7X0VApyBH-zuEmq-ZoxX2abpv4TNZtrNj_XrmneM2&typ
> > > o=1
> > >
> > > -----Original Message-----
> > > From: Sprinklerforum
> > > <[email protected]>
> On
> > > Behalf Of Joe Burtell via Sprinklerforum
> > > Sent: Wednesday, August 25, 2021 3:33 PM
> > > To: [email protected]
> > > Cc: Joe Burtell <[email protected]>
> > > Subject: Fire Pump Backflow
> > >
> > > I have a situation with a verticle in-line fire pump fed from 
> > > water storage tanks. We have a double check backflow installed 
> > > between the
> > tanks
> > > and the fire pump but we don't have enough pressure to open the
> backflow
> > on
> > > the upstream side between the tank and backflow. I talked with 
> > > Watts
> > about
> > > it. They stated there are no backflows with weaker springs. I only 
> > > have about 7 PSI out of the tanks. Has anyone ran into this 
> > > situation before
> > and
> > > have any suggestions to resolve the issue? The engineer suggested
> piping
> > > the jockey pump before the backflow. Not sure how that would work 
> > > in
> > theory.
> > >
> > > Best regards,
> > >
> > > *Joe Burtell, SET, CFPS*
> > >
> > > [image: Burtell Fire_Small]
> > >
> > > Phone | Fax | Mobile| Text *406-204-4653 <++1-406-204-4653>*
> > >
> > > 116 N. 11th Street | Billings, MT 59101
> > >
> > > Email: [email protected]
> > >
> > > Web Site:
> > > https://urldefense.com/v3/__https://linkprotect.cudasvc.com/url?a=
> > > http*3a*2f*2fwww.burtellfire__;JSUl!!B5cixuoO7ltTeg!TTHVu3P9zPjyVb
> > > 6NpB9AS2V987_FU3EZOWFLItv8uvHaNSNBZHRy6nVpsyL8RH7Chg$
> > > .com&c=E,1,mIS0DGsb3z0wjTyb83882uSgINqgEFSGqLh18uWfYKCOnl3nwa2TC-0
> > > fcXvhg0j4XSJsuAWqyMpdtzdHuSJ_WxvO3Q7o-hPO8xm9_oxxdjk7&typo=1
> > >
> > > *“**The bitterness of poor quality remains long after the 
> > > sweetness of
> > low
> > > price is forgotten.**”*
> > >
> > > *NOTICE:*  The information contained in this e-mail transmission 
> > > is intended only for use of the individual or entity named above.
> > > This
> > e-mail
> > > transmission, and any documents, files, previous e-mail 
> > > transmissions
> or
> > > other information attached to it, may contain confidential 
> > > information
> > that
> > > is legally privileged.  If you are not the intended recipient of 
> > > this e-mail transmission, or the employee or agent responsible for
> delivering
> > it
> > > to the intended recipient, you are hereby notified that any 
> > > disclosure, dissemination, distribution, copying or other use of 
> > > this transmission
> or
> > > any of the information contained in or attached to this e-mail is
> > strictly
> > > prohibited.  If you have received this e-mail transmission in 
> > > error,
> > please
> > > immediately notify us by return e-mail transmission and destroy 
> > > the original e-mail transmission as well as its attachments 
> > > without reading
> > or
> > > saving it in any manner.  Thank you.
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > >
> > >
> >
> https://urldefense.com/v3/__https://linkprotect.cudasvc.com/url?a=http
> *3a*2f*2flists.firesprinkler__;JSUl!!B5cixuoO7ltTeg!TTHVu3P9zPjyVb6NpB
> 9AS2V987_FU3EZOWFLItv8uvHaNSNBZHRy6nVpsyJoW5bJeg$
> .org%2flistinfo.cgi%2fsprinklerforum-firesprinkler.org&c=E,1,4VOnCEl3g
> waEY2VAPtM1iKmbiusGFEm9CpR9Cwc6L6nrc5eFjWIs84u1XWaB78YdnoRAJEoRz6SEcMk
> I1-5Hs-32VS2XHchq1XNaGCEHk-InxSBOP5aFm0Rp2Ag,&typo=1
> > >
> > >
> > > --
> > > This email has been checked for viruses by Avast antivirus software.
> > > https://urldefense.com/v3/__https://www.avast.com/antivirus__;!!B5
> > > cixuoO7ltTeg!TTHVu3P9zPjyVb6NpB9AS2V987_FU3EZOWFLItv8uvHaNSNBZHRy6
> > > nVpsyJt3W5gFw$
> > >
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > >
> > >
> >
> https://urldefense.com/v3/__https://linkprotect.cudasvc.com/url?a=http
> *3a*2f*2flists.firesprinkler__;JSUl!!B5cixuoO7ltTeg!TTHVu3P9zPjyVb6NpB
> 9AS2V987_FU3EZOWFLItv8uvHaNSNBZHRy6nVpsyJoW5bJeg$
> .org%2flistinfo.cgi%2fsprinklerforum-firesprinkler.org&c=E,1,96bV5Oi1D
> 8ruAOPq3axsncbM5yDM_93JaNKDzGo8oiQ7zfv_4ItLiBnvAKk8RzW8ABRK3sW3ppZ-LLx
> NIQStHiBKM415_dLxdfVOUfBQgg,,&typo=1
> > >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> >
> https://urldefense.com/v3/__https://linkprotect.cudasvc.com/url?a=http
> *3a*2f*2flists.firesprinkler__;JSUl!!B5cixuoO7ltTeg!TTHVu3P9zPjyVb6NpB
> 9AS2V987_FU3EZOWFLItv8uvHaNSNBZHRy6nVpsyJoW5bJeg$
> .org%2flistinfo.cgi%2fsprinklerforum-firesprinkler.org&c=E,1,idZ_gCy9G
> -ItvigFEBvfRhbxdtfohvvex8-mhTd2SErAZv2umPd-IFMEruYmB9Oc4uftaXc5WnHHVC7
> coiIbqSwv2pGhRDFteGjY1ho5L7whM15pBl3uZg,,&typo=1
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> https://urldefense.com/v3/__https://linkprotect.cudasvc.com/url?a=http
> *3a*2f*2flists.firesprinkler__;JSUl!!B5cixuoO7ltTeg!TTHVu3P9zPjyVb6NpB
> 9AS2V987_FU3EZOWFLItv8uvHaNSNBZHRy6nVpsyJoW5bJeg$
> .org%2flistinfo.cgi%2fsprinklerforum-firesprinkler.org&c=E,1,rmkBt62Bg
> 4EjC7RH56JQsMGVOO_OSY7K9T_lcmqBY9y35srAK0Ulorrd_jJHnaLZFCgNDgBZ7Ypcg5B
> KIriJ42NbWiFR5cxEy41VQL9t&typo=1
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.com/v3/__https://linkprotect.cudasvc.com/url?a=http*3a*2f*2flists.firesprinkler.org*2flistinfo.cgi*2fsprinklerforum-firesprinkler.org&c=E,1,owpJ2vVKG3vmRNCE780smi3mDdQO8j7syKJMQjA-eFq0-CGXRilgPYnoc8i4kGPMVvdkIOnorpN4SKMHhykvE0WDODDyr1lZ7zUY06c5Q3ZTLdlBYv-nORpS&typo=1__;JSUlJSU!!B5cixuoO7ltTeg!TTHVu3P9zPjyVb6NpB9AS2V987_FU3EZOWFLItv8uvHaNSNBZHRy6nVpsyIjXxLg-Q$
_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!TTHVu3P9zPjyVb6NpB9AS2V987_FU3EZOWFLItv8uvHaNSNBZHRy6nVpsyLSgROCKQ$

________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
_______________________________________________
Sprinklerforum mailing list
[email protected]
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwIGaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=88jST93e_Oe8-2XMNGySKXvF1erV-mY3sycrFA20UKA&s=W9OZ4TZmI2l0KXF9C4rX1xaXP_1hl127QOK2E_dq3Ps&e=
 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to