I don't think it would be necessary to connect the fire pump. As Steve 
mentioned, there could be a lot of factors. But, my first thought would be no.



Matt Grise
Alliance Fire Protection
m 913 526 7443
o 913 888 0647
f 913 888 0618

Sent from mobile device


-------- Original message --------
From: Richard Mote via Sprinklerforum <[email protected]>
Date: 8/26/21 7:24 PM (GMT-06:00)
To: [email protected]
Cc: Richard Mote <[email protected]>, [email protected]
Subject: Re: Transfer Switches

This is a building within a building a 60,000 sq.ft. steel building with a 
27,700 sq.ft. freezer. The emergence generator is to protect several tons of 
ice cream from having a melt down. If they size the generator to handle the 
fire 150 hp fire pump load it will double the price he says.


-----Original Message-----
From: Steve Leyton via Sprinklerforum <[email protected]>
To: Richard Mote <[email protected]>; [email protected] 
<[email protected]>
Cc: Steve Leyton <[email protected]>
Sent: Thu, Aug 26, 2021 8:15 pm
Subject: RE: Transfer Switches

To paraphrase, you're asking if it's required to connect a gen set that is 
installed in a building that isn't a high-rise building or some other essential 
facility where there is a code requirement for emergency power, correct?  In 
other words, a voluntary generator with regard to the code set.

Assuming that's the case and there isn't a formal interpretation from the AHJ 
regarding the reliability of the power supply, I would say no.  The code will 
require an emergency power supply or not.  If one is required, then the FLS 
systems have to be on that, but if the secondary isn't required by code then 
it's up to the owner (and let's face it, that's certainly a good idea if the 
generator is sized for the fire pump).    So there MAY be something in the code 
that requires this, but only if it's a mandatory generator.


Steve Leyton

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Richard Mote via Sprinklerforum
Sent: Thursday, August 26, 2021 5:04 PM
To: [email protected]
Cc: Richard Mote <[email protected]>
Subject: Transfer Switches

Got a email from a customer with the following question. I'm on the road with 
no access to my books.If an emergency generator is installed on a building, is 
there anything in the codes that would require it to be connected to the fire 
pump.
RichardL. Mote CET

Rimrock Design Services,LLC

PO Box 36
Middleburg, PA 17842

Mobile 570-541-2685

EMAIL [email protected]


_______________________________________________
Sprinklerforum mailing list
[email protected]
https://linkprotect.cudasvc.com/url?a=http%3a%2f%2flists.firesprinkler.org%2flistinfo.cgi%2fsprinklerforum-firesprinkler.org&c=E,1,xsDfg13sH1rVvmFMge6n6ESXNOcF7Aca3kOIxUdskrpsjtdnop9kzorj-4lCqWb_3RXhvTDT1GxRmHzFJpZrGXuA5-4AVYrUIxODsAAJcpVEji8q7A4Wy1fiw_0,&typo=1
_______________________________________________
Sprinklerforum mailing list
[email protected]
https://linkprotect.cudasvc.com/url?a=http%3a%2f%2flists.firesprinkler.org%2flistinfo.cgi%2fsprinklerforum-firesprinkler.org&c=E,1,Z3O7tW2PNyEduWAolb9hYJTCVvCZkRz0UXTMEuDB860Gxgoq6YXV45C7kLfPL5QStFnGk6YaBPgH2SNK6FIiGt8oIlfb5pLRdcaRWRk3acZp&typo=1
_______________________________________________
Sprinklerforum mailing list
[email protected]
https://linkprotect.cudasvc.com/url?a=http%3a%2f%2flists.firesprinkler.org%2flistinfo.cgi%2fsprinklerforum-firesprinkler.org&c=E,1,gtHuOSaDm9oH_sBnzIEoOrHaUQZtEz8yuoByShgc9Z3JcckJmAUMNl3NzKRuIoyZylS9V3MhObMflOvnKDFBl26stp88HDZ7lS3EHKHsgXaBPdDcybSoyFjm1HkV&typo=1
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to