It's ice cream; depending on local health code requirements, a "save" might 
still be a profound or total loss.

After a long time in this racket, I find myself falling back more and more on 
Chapter 1 of all the standards wherein we find the intent statement, which is 
to provide a "reasonable" level of protection against fire.    If they 
want/need a generator to keep ice cream from melting in this fully sprinklered 
building, then plug one in.   But it's also fair to undertake a cost/benefit 
analysis if backing up the pump means doubling the cost of the gen set and if 
the owner doesn't see the value, so be it.  Keeping in mind that at no point in 
this discussion has there been any allusion to the power supply not meeting the 
reliability requirements of NFPA 20.

SL


From: Mark Phillips [mailto:[email protected]]
Sent: Friday, August 27, 2021 3:48 AM
To: Richard Mote <[email protected]>; [email protected]
Cc: Richard Mote <[email protected]>; Steve Leyton <[email protected]>
Subject: Re: Transfer Switches

Not a code requirement but less expensive that complete product loss.



Sent from my mobile device
Please excuse spelling, grammar, and auto correction.

Mark Phillips
Branch Manager
Fire Sprinkler Design, Install, Inspections
Service, Backflows, Fire Alarm Inspections

832-101 Purser Drive
Raleigh NC 27603
Phone: 919-779-4010
Fax : 919-779-4014
Cell : 919-268-7587
Email : [email protected]<mailto:[email protected]>
Web : www.pyebarkerfire.com<http://www.pyebarkerfire.com>

________________________________
From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 on behalf of Richard Mote via Sprinklerforum 
<[email protected]<mailto:[email protected]>>
Sent: Thursday, August 26, 2021 8:24:16 PM
To: 
[email protected]<mailto:[email protected]>
 
<[email protected]<mailto:[email protected]>>
Cc: Richard Mote <[email protected]<mailto:[email protected]>>; 
[email protected]<mailto:[email protected]> 
<[email protected]<mailto:[email protected]>>
Subject: Re: Transfer Switches

[EXTERNAL]

This is a building within a building a 60,000 sq.ft. steel building with a 
27,700 sq.ft. freezer. The emergence generator is to protect several tons of 
ice cream from having a melt down. If they size the generator to handle the 
fire 150 hp fire pump load it will double the price he says.


-----Original Message-----
From: Steve Leyton via Sprinklerforum 
<[email protected]<mailto:[email protected]>>
To: Richard Mote <[email protected]<mailto:[email protected]>>; 
[email protected]<mailto:[email protected]>
 
<[email protected]<mailto:[email protected]>>
Cc: Steve Leyton <[email protected]<mailto:[email protected]>>
Sent: Thu, Aug 26, 2021 8:15 pm
Subject: RE: Transfer Switches

To paraphrase, you're asking if it's required to connect a gen set that is 
installed in a building that isn't a high-rise building or some other essential 
facility where there is a code requirement for emergency power, correct?  In 
other words, a voluntary generator with regard to the code set.

Assuming that's the case and there isn't a formal interpretation from the AHJ 
regarding the reliability of the power supply, I would say no.  The code will 
require an emergency power supply or not.  If one is required, then the FLS 
systems have to be on that, but if the secondary isn't required by code then 
it's up to the owner (and let's face it, that's certainly a good idea if the 
generator is sized for the fire pump).    So there MAY be something in the code 
that requires this, but only if it's a mandatory generator.


Steve Leyton

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Richard Mote via Sprinklerforum
Sent: Thursday, August 26, 2021 5:04 PM
To: 
[email protected]<mailto:[email protected]>
Cc: Richard Mote <[email protected]<mailto:[email protected]>>
Subject: Transfer Switches

Got a email from a customer with the following question. I'm on the road with 
no access to my books.If an emergency generator is installed on a building, is 
there anything in the codes that would require it to be connected to the fire 
pump.
RichardL. Mote CET

Rimrock Design Services,LLC

PO Box 36
Middleburg, PA 17842

Mobile 570-541-2685

EMAIL [email protected]<mailto:[email protected]>


_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to