At that point it is probably a discussion to have with your facility insurance 
carrier...



(not that I wouldn't sell them a full diesel motor backup if they asked real 
nice! 😊)



Matt





-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Mark Phillips via Sprinklerforum
Sent: Friday, August 27, 2021 5:48 AM
To: Richard Mote <[email protected]>; [email protected]
Cc: Mark Phillips <[email protected]>; Richard Mote 
<[email protected]>; [email protected]
Subject: Re: Transfer Switches



Not a code requirement but less expensive that complete product loss.







Sent from my mobile device

Please excuse spelling, grammar, and auto correction.



Mark Phillips

Branch Manager

Fire Sprinkler Design, Install, Inspections Service, Backflows, Fire Alarm 
Inspections



832-101 Purser Drive

Raleigh NC 27603

Phone: 919-779-4010

Fax : 919-779-4014

Cell : 919-268-7587

Email : [email protected]<mailto:[email protected]>

Web : 
https://linkprotect.cudasvc.com/url?a=https%3a%2f%2fwww.pyebarkerfire.com&c=E,1,sP8puY5rWtdm-dIYv95PjYwkAu5WOERngCxq_3Ro1bRBk4wGAmJXKK41TqcLyZhAOajD6KmGE91-I9CKuntD7Ce0nNtU1UobpCkV9W_3iJdDpT7kJMEguAY4amE,&typo=1



________________________________

From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 on behalf of Richard Mote via Sprinklerforum 
<[email protected]<mailto:[email protected]>>

Sent: Thursday, August 26, 2021 8:24:16 PM

To: 
[email protected]<mailto:[email protected]>
 
<[email protected]<mailto:[email protected]>>

Cc: Richard Mote <[email protected]<mailto:[email protected]>>; 
[email protected]<mailto:[email protected]> 
<[email protected]<mailto:[email protected]>>

Subject: Re: Transfer Switches



[EXTERNAL]



This is a building within a building a 60,000 sq.ft. steel building with a 
27,700 sq.ft. freezer. The emergence generator is to protect several tons of 
ice cream from having a melt down. If they size the generator to handle the 
fire 150 hp fire pump load it will double the price he says.





-----Original Message-----

From: Steve Leyton via Sprinklerforum 
<[email protected]<mailto:[email protected]>>

To: Richard Mote <[email protected]<mailto:[email protected]>>; 
[email protected]<mailto:[email protected]>
 
<[email protected]<mailto:[email protected]>>

Cc: Steve Leyton <[email protected]<mailto:[email protected]>>

Sent: Thu, Aug 26, 2021 8:15 pm

Subject: RE: Transfer Switches



To paraphrase, you're asking if it's required to connect a gen set that is 
installed in a building that isn't a high-rise building or some other essential 
facility where there is a code requirement for emergency power, correct?  In 
other words, a voluntary generator with regard to the code set.



Assuming that's the case and there isn't a formal interpretation from the AHJ 
regarding the reliability of the power supply, I would say no.  The code will 
require an emergency power supply or not.  If one is required, then the FLS 
systems have to be on that, but if the secondary isn't required by code then 
it's up to the owner (and let's face it, that's certainly a good idea if the 
generator is sized for the fire pump).    So there MAY be something in the code 
that requires this, but only if it's a mandatory generator.





Steve Leyton



-----Original Message-----

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Richard Mote via Sprinklerforum

Sent: Thursday, August 26, 2021 5:04 PM

To: 
[email protected]<mailto:[email protected]>

Cc: Richard Mote <[email protected]<mailto:[email protected]>>

Subject: Transfer Switches



Got a email from a customer with the following question. I'm on the road with 
no access to my books.If an emergency generator is installed on a building, is 
there anything in the codes that would require it to be connected to the fire 
pump.

RichardL. Mote CET



Rimrock Design Services,LLC



PO Box 36

Middleburg, PA 17842



Mobile 570-541-2685



EMAIL [email protected]<mailto:[email protected]>





_______________________________________________

Sprinklerforum mailing list

[email protected]<mailto:[email protected]>

https://linkprotect.cudasvc.com/url?a=http%3a%2f%2flists.firesprinkler.org%2flistinfo.cgi%2fsprinklerforum-firesprinkler.org&c=E,1,qqmHC90XY8uf9k-0SwKefgYEP5z1I40_V0CW2m450ETsEE_8QimrKWs3yG1jCyNq4c7KWjHFI-zHoPZoqhwOe2x8VHbICGX5dgsKw3yRI_Dl5qTUDHvTEDgEqkc,&typo=1

_______________________________________________

Sprinklerforum mailing list

[email protected]<mailto:[email protected]>

https://linkprotect.cudasvc.com/url?a=http%3a%2f%2flists.firesprinkler.org%2flistinfo.cgi%2fsprinklerforum-firesprinkler.org&c=E,1,7cfoQktSUYcbNEtvC5x0_aifyIy3oPN5hFeNYP0I98zKbQw0GwDoXXkRW_1_M_fLdy4j2Y0Wsr8CTRHyz_YehrphUoeI2eNc7nIPa6qwOZCMWbPzevzD__nrLpk,&typo=1

_______________________________________________

Sprinklerforum mailing list

[email protected]<mailto:[email protected]>

https://linkprotect.cudasvc.com/url?a=http%3a%2f%2flists.firesprinkler.org%2flistinfo.cgi%2fsprinklerforum-firesprinkler.org&c=E,1,5o42EfomzIjQ1nFU3Fna8inIO-l0N1ZSItyhnj7zO_xJFmmU-uMDcyJXlxZ9cHsGkdotDBAfH-tOgeEiuinmgI-1k46wAEtKqF7XZfskqh--dyJh4rHgjA,,&typo=1

_______________________________________________

Sprinklerforum mailing list

[email protected]<mailto:[email protected]>

https://linkprotect.cudasvc.com/url?a=http%3a%2f%2flists.firesprinkler.org%2flistinfo.cgi%2fsprinklerforum-firesprinkler.org&c=E,1,c91Bu9D4lLiu2L-_7B7cRnQ0MaVJTz6dG95gZjUgAMuoi8PgME26olE_8HqV80cMBGzSdpc-tgPgvpxmU7oK5VVfREjpJeNMMdwv8WiyLhd7bOAv18_-48Qv&typo=1
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to