Indeed Travis and I have journeyed down this road before, one time in
particular.
An AHJ, who happened to be a registered PE, AND the state fire marshal
was insisting that Travis' design would not be accepted using CCS
sprinklers, and that standard spray QR's be used, even though that use
was contrary to -13, and their listing.
If I remember the remarks of the AHJ correctly, when politely - VERY
politely - challenged by Travis, his response was, "Just do what I tell
you, that would make it so much more simple."
some times I just shake my head,
*Ken Wagoner, SET*
*Parsley Consulting
500 West Mechanic Street
Harrisonville, Missouri 64701-2235*
*Phone: (760) 745-6181 *
*Visit the website
<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.parsleyconsulting.com%2f&c=E,1,Y5zKJKPEh1mBEBqSR-VE9cUKl5y-eyP8BpvmE_5j9ZqW2eJbNphYzrCMBZ-2YuX6d-RRkHI4gQ1FV-cvOeCfRC58uZS9NiToZv2mx7909oCqLvCW_n5hDHeK&typo=1>*
On 1/11/2022 3:07 PM, Travis Mack via Sprinklerforum wrote:
It says specifically listed. That means you must use specifically listed
sprinklers. How deep is the space? Is it flat or sloped? If it meets the
criteria for the specially listed, then that is what you use. Ive been down
this road many times.
Travis Mack, CFPS, CWBSP, RME-G, COC, SET
Senior Engineering Manager
MFP Design
480-505-9271 ext. 700 C: 480-272-2471
[email protected]<mailto:[email protected]>
www.mfpdesign.com<http://www.mfpdesign.com>
Send large files to us
via:https://www.hightail.com/u/MFPDesign<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>
From: Sprinklerforum<[email protected]> On Behalf
Of Trillium Fire Sprinkler Design INC via Sprinklerforum
Sent: Tuesday, January 11, 2022 2:05 PM
To:[email protected]
Cc: Trillium Fire Sprinkler Design INC<[email protected]>
Subject: RE: COMBUSTIBLE CONCEALED SPACE
My question is: Are QR uprights listed to be used in those areas or does it
have to be a CCS sprinkler?
Troy
-----Original Message-----
From: Sprinklerforum
<[email protected]<mailto:[email protected]>>
On
Behalf Of Tom Wellen via Sprinklerforum
Sent: January 11, 2022 3:56 PM
To:[email protected]<mailto:[email protected]>
Cc: Tom Wellen <[email protected]<mailto:[email protected]>>; Trillium Fire
Sprinkler Design INC
<[email protected]<mailto:[email protected]>>
Subject: Re: COMBUSTIBLE CONCEALED SPACE
Troy,
No. NFPA 13, 2019 edition in 9.3.2 is specific that sprinklers are listed
for horizontal combustible concealed spaces. Specifically listed to provide
protection.....
On Tue, Jan 11, 2022 at 2:40 PM Trillium Fire Sprinkler Design INC via
Sprinklerforum
<[email protected]<mailto:[email protected]>>
wrote:
Can someone confirm that it is not mandatory to use CCS sprinklers in
a space 36" or less?
I know it allows for larger spacing, but code wise. I don't believe
they are a must and the space can be protected with QR uprights.
Regards
Troy S
_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl<http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl>
er.org
--
Tom Wellen - May '91
Senior Fire Protection Consultant
Fire Engineering & Consulting, LLC
(972) 355-2159
fireeac.com
<http://fireeac.com/<http://fireeac.com>>
_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org<http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org>
_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org<http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org