On Wed, Jan 12, 2022 at 7:13 AM Ken Wagoner via Sprinklerforum <
sprinklerforum@lists.firesprinkler.org> wrote:

> Indeed Travis and I have journeyed down this road before, one time in
> particular.
>
> An AHJ, who happened to be a registered PE, AND the state fire marshal
> was insisting that Travis' design would not be accepted using CCS
> sprinklers, and that standard spray QR's be used, even though that use
> was contrary to -13, and their listing.
>
> If I remember the remarks of the AHJ correctly, when politely - VERY
> politely - challenged by Travis, his response was, "Just do what I tell
> you, that would make it so much more simple."
>
> some times I just shake my head,
> *Ken Wagoner, SET*
> *Parsley Consulting
> 500 West Mechanic Street
> Harrisonville, Missouri 64701-2235*
> *Phone: (760) 745-6181 *
> *Visit the website
> <
> https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.parsleyconsulting.com%2f&c=E,1,Y5zKJKPEh1mBEBqSR-VE9cUKl5y-eyP8BpvmE_5j9ZqW2eJbNphYzrCMBZ-2YuX6d-RRkHI4gQ1FV-cvOeCfRC58uZS9NiToZv2mx7909oCqLvCW_n5hDHeK&typo=1>*
>
>
> On 1/11/2022 3:07 PM, Travis Mack via Sprinklerforum wrote:
> > It says specifically listed.  That means you must use specifically
> listed sprinklers.  How deep is the space?  Is it flat or sloped?  If it
> meets the criteria for the specially listed, then that is what you use.
> Ive been down this road many times.
> >
> > Travis Mack, CFPS, CWBSP, RME-G, COC, SET
> > Senior Engineering Manager
> > MFP Design
> > 480-505-9271 ext. 700 C: 480-272-2471
> > travis.m...@mfpdesign.com<mailto:travis.m...@mfpdesign.com>
> > www.mfpdesign.com<http://www.mfpdesign.com>
> >
> > Send large files to us via:https://www.hightail.com/u/MFPDesign<
> https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0
> >
> >
> > From: Sprinklerforum<sprinklerforum-boun...@lists.firesprinkler.org>
> On Behalf Of Trillium Fire Sprinkler Design INC via Sprinklerforum
> > Sent: Tuesday, January 11, 2022 2:05 PM
> > To:sprinklerforum@lists.firesprinkler.org
> > Cc: Trillium Fire Sprinkler Design INC<trilliumf...@cwisp.ca>
> > Subject: RE: COMBUSTIBLE CONCEALED SPACE
> >
> > My question is: Are QR uprights listed to be used in those areas or does
> it
> > have to be a CCS sprinkler?
> >
> > Troy
> >
> > -----Original Message-----
> > From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org
> <mailto:sprinklerforum-boun...@lists.firesprinkler.org>> On
> > Behalf Of Tom Wellen via Sprinklerforum
> > Sent: January 11, 2022 3:56 PM
> > To:sprinklerforum@lists.firesprinkler.org<mailto:
> sprinklerforum@lists.firesprinkler.org>
> > Cc: Tom Wellen <tgwel...@gmail.com<mailto:tgwel...@gmail.com>>;
> Trillium Fire Sprinkler Design INC
> > <trilliumf...@cwisp.ca<mailto:trilliumf...@cwisp.ca>>
> > Subject: Re: COMBUSTIBLE CONCEALED SPACE
> >
> > Troy,
> >
> > No. NFPA 13, 2019 edition in 9.3.2 is specific that sprinklers are listed
> > for horizontal combustible concealed spaces. Specifically listed to
> provide
> > protection.....
> >
> >
> >
> >
> > On Tue, Jan 11, 2022 at 2:40 PM Trillium Fire Sprinkler Design INC via
> > Sprinklerforum <sprinklerforum@lists.firesprinkler.org<mailto:
> sprinklerforum@lists.firesprinkler.org>> wrote:
> >
> >> Can someone confirm that it is not mandatory to use CCS sprinklers in
> >> a space 36" or less?
> >>
> >>
> >>
> >> I know it allows for larger spacing, but code wise. I don't believe
> >> they are a must and the space can be protected with QR uprights.
> >>
> >>
> >>
> >> Regards
> >>
> >>
> >>
> >> Troy S
> >>
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> Sprinklerforum@lists.firesprinkler.org<mailto:
> Sprinklerforum@lists.firesprinkler.org>
> >>
> >> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl<
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl>
> >> er.org
> >>
> >
> > --
> > Tom Wellen - May '91
> > Senior Fire Protection Consultant
> > Fire Engineering & Consulting, LLC
> > (972) 355-2159
> > fireeac.com
> >
> > <http://fireeac.com/<http://fireeac.com>>
> > _______________________________________________
> > Sprinklerforum mailing list
> > Sprinklerforum@lists.firesprinkler.org<mailto:
> Sprinklerforum@lists.firesprinkler.org>
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> <
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > Sprinklerforum@lists.firesprinkler.org<mailto:
> Sprinklerforum@lists.firesprinkler.org>
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> <
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > Sprinklerforum@lists.firesprinkler.org
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>