When there is a will, there is a way. The paddle-type water flow device can be 
installed in a small parallel byp[ass run of this suction line with an 
appropriate large hole strainer, supervised maintenance valves and all the 
trimmings. Engineer it so that it gets enough flow  through this bypass section 
to trip the indicator. It is a solution to the detachment concern. You guys 
have seen this concept used all the time in the water company’s equipment. Come 
on now. I am not endorsing the requirement, just saying there is a logical way 
to detect flow this way.

> 
>> On Aug 5, 2022 at 9:36 AM, <Taylor Schumacher 
>> <mailto:[email protected]>> wrote:
>> 
>> Does anyone have any experience with a paddle-type water flow detector in 
>> the suction line of a fire pump?
>>  
>> I have a long section of pipe between my backflow preventer and the suction 
>> flange of my pump that a plan reviewer wants supervised. I get the concern, 
>> but I have concerns with the paddle in the suction piping.
>>  
>> Any thoughts or experiences are greatly appreciated.
>> 