Just out of curiosity - who does this plan reviewer work for? Is it an owner's 
rep/engineer/insurance rep or a city code official?

Matt


From: Taylor Schumacher <[email protected]>
Sent: Friday, August 05, 2022 9:43 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: WFD In Pump Suction Line

I thought about using the turbulence distances as a good practice. I have over 
200 feet of pipe so the turbulence would not be a factor.

The likelihood of the paddle becoming lodged and blocking water supply or worse 
getting sucked into the pump is the concern.

We all know there is no code requirement for that installation.

For what it's worth, the pipe is traveling in a parking garage.


Taylor Schumacher ET



From: Matt Grise <[email protected]<mailto:[email protected]>>
Sent: Friday, August 05, 2022 8:45 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: WFD In Pump Suction Line

I get the concern also - but the request seems to be in direct contradiction to 
the code. And it introduces a paddle that could jam in the pipe or detach from 
the switch and flow into the pump.

Many plan reviewers are limited to enforcing codes, not enforcing their 
personal preferences. Can they produce a code section that requires monitoring 
in this portion of the system?

There are ways to detect flow without a paddle sensor - maybe an alternate 
detection method? If it must be there, I would say at least 50' upstream of the 
pump similar to a butterfly valve.

Matt


From: Taylor Schumacher <[email protected]<mailto:[email protected]>>
Sent: Friday, August 05, 2022 8:35 AM
To: '[email protected]' 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] WFD In Pump Suction Line

Does anyone have any experience with a paddle-type water flow detector in the 
suction line of a fire pump?

I have a long section of pipe between my backflow preventer and the suction 
flange of my pump that a plan reviewer wants supervised. I get the concern, but 
I have concerns with the paddle in the suction piping.

Any thoughts or experiences are greatly appreciated.


Taylor Schumacher ET