NFPA 13   2019 edition
9.4.3 - 9.4.3.6

handbook  also has some comments
FAQ
9.4.3.2

Chuck Bamford SET



On Mon, Sep 26, 2022 at 9:43 AM Fpdcdesign <[email protected]> wrote:

> I am working on to an addition to an existing system that has Tyco EC-11
> pendent sprinklers. According to the data sheet, these sprinklers may be QR
> in some circumstances and SR in others. The addition I am working on will
> be using standard coverage sprinklers. The space is open to the area with
> the EC-11 sprinklers but separated by a deep soffit. The design of the
> EC-11 is such that they are considered standard response by the listing.
> The obvious question is QR or SR for the new sprinklers? I am assuming QR
> because that is closer to the response time of the EC-11s despite the SR
> listing, but I am being questioned on this. Thoughts?
>
> Todd G Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> 860-535-2080 (ofc)
> 860-554-7054  (fax)
> 860-608-4559 (cell)
>