No, all quick response sprinklers are fast response, but not all fast response 
are quick response.

When we had this come up in the early 2000’s, I was directed by an AFSA 
informal interp to match the response elements.  Again, in our case it was ESFR 
adjacent to EC sprinklers.  The EC were 20x20 and not QR for that spacing.  It 
was determined that since the response elements of both were fast response then 
we would be OK in that scenario.

Please rate our customer 
service<https://survey.medallia.com/?emailsignature&fc=3539&bg=Fire%20and%20Fabrication>

Travis Mack, RME-G, COC, SET
Senior Engineering Manager
MFP Design
480-505-9271 ext. 700 C: 480-272-2471
[email protected]<mailto:[email protected]>
[email protected]
www.mfpdesign.com<http://www.mfpdesign.com>

Send large files to us via: 
https://www.hightail.com/u/MFPDesign<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>

From: Ron Greenman <[email protected]>
Sent: Tuesday, September 27, 2022 11:04 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: Adding sprinklers to system with mixed SR/QR 
listing

Fast response elements do not universally equate to quick response sprinklers.

https://www.vikinggroupinc.com/sites/default/files/documents/Automatic%20Sprinkler%20Thermal%20Sensitivity.pdf<https://www.vikinggroupinc.com/sites/default/files/documents/Automatic%20Sprinkler%20Thermal%20Sensitivity.pdf>

On Tue, Sep 27, 2022 at 10:58 AM Matthew J Willis 
<[email protected]<mailto:[email protected]>> wrote:
Todd,

What are you protecting?

The wording for extending one hazard into another is a sufficient heat barrier.

You may be chasing rabbits.

R/
Matt


Matthew J. Willis, CWBSP
Design Manager

Rapid Fire Protection, Inc.
600 E. Carlson St. Suite AB | Cheyenne, WY. 82009
Office (307) 426-4077 ext. 404
Direct (307) 316-6630
Cell (605) 391-2733
[cid:[email protected]]


From: Fpdcdesign <[email protected]<mailto:[email protected]>>
Sent: Tuesday, September 27, 2022 11:04 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: Adding sprinklers to system with mixed SR/QR 
listing

Compartment does not apply here.

The conclusion I and coming to is that we need to closely match the RTI of the 
new sprinklers to the RTI of the EC sprinkler, regardless of how the latter is 
listed.



On Sep 27, 2022 at 8:15 AM, <Sean 
Conlin<mailto:[email protected]>> wrote:
If the EC sprinkler used is listed as QR in its current application, then the 
new area of work has to use QR unless the area of work is located in a separate 
compartment.   Check the definition of compartment to see if the soffit you 
mention can work for you.

Regards,

Sean W Conlin
Demand Sprinkler Design Inc.
37 Summerfield Crescent
Brampton, ON L6X 4K4
P: 905 216-0922


On Sep 26, 2022, at 12:42 PM, Fpdcdesign 
<[email protected]<mailto:[email protected]>> wrote:

I am working on to an addition to an existing system that has Tyco EC-11 
pendent sprinklers. According to the data sheet, these sprinklers may be QR in 
some circumstances and SR in others. The addition I am working on will be using 
standard coverage sprinklers. The space is open to the area with the EC-11 
sprinklers but separated by a deep soffit. The design of the EC-11 is such that 
they are considered standard response by the listing. The obvious question is 
QR or SR for the new sprinklers? I am assuming QR because that is closer to the 
response time of the EC-11s despite the SR listing, but I am being questioned 
on this. Thoughts?

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080<tel:860-535-2080> (ofc)
860-554-7054<tel:860-554-7054>  (fax)
860-608-4559<tel:860-608-4559> (cell)

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org>
To unsubscribe send an email to 
[email protected]<mailto:[email protected]>
_________________________________________________________ SprinklerForum 
mailing list: 
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org>
 To unsubscribe send an email to 
[email protected]<mailto:[email protected]>

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org>
To unsubscribe send an email to 
[email protected]<mailto:[email protected]>
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to