NFPA 13 (2016 edition) 8.16.2.5.3.6 Tie-in drains shall be provided for 
multiple adjacent trapped branch pipes and shall be only 1 in. (25 mm). Tie-in 
drain lines shall be pitched a minimum of 1⁄2 in. per 10 ft (4 mm/m).



David L. Miller, P.E.
Engineered Fire Protection, LLC
11920 Richcroft Avenue
Baton Rouge, Louisiana  70814
225-273-5040

-----Original Message-----
From: Sean Lockyer <[email protected]> 
Sent: Monday, March 13, 2023 6:31 PM
To: [email protected]
Subject: [Sprinklerforum] Combining dry system drains

Can dry system drains (I.E. - Drum drips) be combined or interconnected ?

            Sean Lockyer
            Project Designer                                   
            AITLifeSafety                