Now that is interesting…

 

The wording of the code is that tie-in drains are required, but the commentary 
says they should be avoided if possible.

 

The 2022 edition (16.10.5.3.6) has the same wording in both the code and the 
commentary.

 

 

David L. Miller, P.E.

Engineered Fire Protection, LLC

11920 Richcroft Avenue

Baton Rouge, Louisiana  70814

225-273-5040

 

From: [email protected] <[email protected]> 
Sent: Monday, March 13, 2023 6:41 PM
To: [email protected]
Subject: [Sprinklerforum] Re: Combining dry system drains

 

2016 edition NFPA 13 8.16.2.5.3.6 ….. commentary from handbook…..Tie-in drains 
on multiple adjacent branch lines should be avoided, if possible, because the 
use of tie-in drains, in effect, creates a gridded system

 

 

Jeff Normand

 

 

From: [email protected] <mailto:[email protected]>  <[email protected] 
<mailto:[email protected]> > 
Sent: Monday, March 13, 2023 6:37 PM
To: 'Discussion list on issues relating to automatic fire sprinklers' 
<[email protected] 
<mailto:[email protected]> >
Subject: [Sprinklerforum] Re: Combining dry system drains

 

NFPA 13 (2016 edition) 8.16.2.5.3.6 Tie-in drains shall be provided for 
multiple adjacent trapped branch pipes and shall be only 1 in. (25 mm). Tie-in 
drain lines shall be pitched a minimum of 1⁄2 in. per 10 ft (4 mm/m).



David L. Miller, P.E.
Engineered Fire Protection, LLC
11920 Richcroft Avenue
Baton Rouge, Louisiana 70814
225-273-5040

-----Original Message-----
From: Sean Lockyer <[email protected] 
<mailto:[email protected]> > 
Sent: Monday, March 13, 2023 6:31 PM
To: [email protected] 
<mailto:[email protected]> 
Subject: [Sprinklerforum] Combining dry system drains

Can dry system drains (I.E. - Drum drips) be combined or interconnected ?

Sean Lockyer
Project Designer 
AITLifeSafety 




_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected] 
<mailto:[email protected]> 

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected] 
<mailto:[email protected]> 

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to