0.434 vs 0.433, U of M. Something to do with measurement of mass in the 
proximity of turtles. I don’t get it either.
 
bv

> On 11/02/2023 6:00 AM PDT Bob Caputo <[email protected]> wrote:
>  
>  
> 
> Lets look at this from the practical application side of things.  The 
> standpipe and its valves are there for the fire service, solely and only.  
> Every department has its own operational standards, due in part to the hose 
> nozzles they choose.  Some want the hose valves at intermediate landings, 
> some want them on the floor landing.  Some want 100 psi, while others want 
> 125 psi at the hose valve (because there is about 29 psi appliance loss in 
> 100 ft of hose) and they want 100 psi at the nozzle.
> 
>  
> 
> Here on earth, the pressure of elevation is the same for everyone:  0.433 psi 
> per ft of elevation – that is unless you went to the University of Maryland, 
> where its 0.434 psi per ft. 😉
> 
>  
> 
> Some departments want the FDC on the address side of the building, while 
> others may want more than one FDC for a high rise that is built on an entire 
> city block.  Getting back to the point…  NFPA 14 is a minimum standard for 
> the design and installation of standpipes which will be used by the first 
> responders – who should be the only one’s deciding the design criteria and 
> the location of equipment to be used in fighting fires.
> 
>  
> 
> That’s my 2 cents – I hope that helps.
> 
>  
> 
> bc
> 
>  
> 
>  
> 
> Bob Caputo, CFPS
> 
> President
> 
> American Fire Sprinkler Association
> 
> c:     760-908-7753 tel:760-908-7753
> 
> p:
> 
> 214-349-5965 tel:214-349-5965 ext124
> 
> w:
> 
> firesprinkler.org http://firesprinkler.org/   
> https://www.facebook.com/firesprinkler.org/
> 
>    https://twitter.com/afsa/status/1039528345367732224   
> https://www.linkedin.com/company/american-fire-sprinkler-association-afsa-/   
> https://www.instagram.com/firesprinklerorg/
> 
>  
> 
> Sprinkler Hydraulic Calculations Workshop
> 
>  
> 
> AFSA’s three-day, in-person workshop provides a deep dive into the principles 
> of hydraulics, including the different types of pressure, calculating changes 
> in pressure (elevation and friction loss), and node analysis. Click here 
> https://www.firesprinkler.org/programs/calculations/ for details and to 
> register.
> 
> 
> 
>  
> 
> From: Kyle.Montgomery <[email protected] 
> mailto:[email protected]>
> Sent: Wednesday, November 1, 2023 6:21 PM
> To: Discussion list on issues relating to automatic fire sprinklers 
> <[email protected] 
> mailto:[email protected]>
> Subject: [Sprinklerforum] Re: [EXTERNAL] Re: Pressure Regulating Valves 
> Residual Pressures
> 
>  
> 
> Well, they can’t have a minimum of 100 psi AND a maximum of 100 psi available 
> at the hose valve. So, if they want to limit the residual pressure to a 
> maximum of 100 psi, then they need to deviate from NFPA 14 and allow LESS 
> THAN 100 psi as the minimum.
> 
>  
> 
> [Note: I suppose that maybe you could utilize a pilot-operated 
> pressure-regulating valve at every hose valve location to keep the pressure 
> right at 100 psi over a wide range of flow, but that would be unorthodox to 
> say the least.]
> 
>  
> 
> Kyle Montgomery
> 
>  
> 
> Aero Automatic Sprinkler Co.
> 
> 21605 N. Central Ave.
> 
> Phoenix, AZ 85024
> 
> Direct: 623.580.7820 tel:623.580.7820
> 
> Cell: 602.763.4736 tel:602.763.4736
> 
> [email protected] mailto:[email protected]
> 
>  
> 
>  
> 
>  
> 
> From: Greg McGahan <[email protected] 
> mailto:[email protected]>
> Sent: Tuesday, October 31, 2023 9:16 AM
> To: Discussion list on issues relating to automatic fire sprinklers 
> <[email protected] 
> mailto:[email protected]>
> Subject: [EXTERNAL] [Sprinklerforum] Re: Pressure Regulating Valves Residual 
> Pressures
> 
>  
> 
> With all due respect Rick, I have had Fire Departments very concerned about 
> the residual pressure being greater than 100 psi for safety. Sizing PRV's is 
> not the easiest part of a standpipe design. If you are in a jurisdiction that 
> requires
> 
>  
> 
> With all due respect Rick, I have had Fire Departments very concerned about 
> the residual pressure being greater than 100 psi for safety. 
> 
>  
> 
> Sizing PRV's is not the easiest part of a standpipe design. If you are in a 
> jurisdiction that requires flow testing and recording the pressures prior to 
> the final inspection (as it should be per NFPA 14), guessing could cost a lot 
> of money to correct. 
> 
>  
> 
> On Tue, Oct 31, 2023 at 10:49 AM Rick Matsuda <[email protected] 
> mailto:[email protected]> wrote:
> 
> > 
> > The requirements of NFPA-14 for the standpipe hose valves are maximum 
> > 175-psi static outlet pressure and minimum 100-psi residual outlet pressure 
> > while flowing 250-gpm through the hose valve. 
> > If your pump source is from the city mains, then make it easy on yourself 
> > and select a PRV hose valve that will provide maximum 165-psi static outlet 
> > pressure. 
> > This should allow you to use whatever residual inlet pressure while flowing 
> > the 750-gpm total standpipe demand and still provide the minimum 100-psi 
> > residual outlet pressure. 
> > 
> > I used the 165-psi static outlet pressure cause the pump inlet pressure may 
> > vary up/down which will vary the pump static outlet pressure which may 
> > raise the static outlet pressure over 175-psi. 
> > 
> > If the pump source has a constant pressure like an elevated tank, then 
> > select a PRV that will provide a maximum 175-psi outlet pressure. 
> > 
> > Just my opinion but if you select a PRV based on the maximum static outlet 
> > pressure then this should allow a bit more than the 100-psi minimum outlet 
> > pressure. Check the charts to verify this. 
> > Don’t select a PRV based on providing just the minimum outlet pressure. 
> > I think that the fire department will appreciate any extra pressure to 
> > offset the friction loss through their fire hoses.
> > Rick Matsuda
> > 
> >  
> > 
> > > 
> > > On Oct 31, 2023, at 7:24 AM, Eric Rieve <[email protected] 
> > > mailto:[email protected]> wrote:
> > > 
> > 
> > > 
> > >  
> > > 
> > > Micah,
> > > 
> > >  
> > > 
> > > Looking at the spec sheet from Zurn I agree with Travis that you use your 
> > > expected residual pressure while flowing the full system demand of 
> > > 750gpm. I haven’t installed this valve myself, but you’ll notice on the 
> > > residual pressure charts that the bonnet type curve lines stop well below 
> > > 175psi. So, while you may pick a 120psi outlet pressure while flowing 
> > > 750gpm, the extra play in the curve should allow the valve to maintain an 
> > > outlet pressure below 175psi when being tested individually at 250gpm.
> > > 
> > >  
> > > 
> > > Hope this helps!
> > > 
> > > Eric Rieve, SET
> > > 
> > > Rieve Fire Protection
> > > 
> > >  
> > > 
> > > From: Micah Davis <[email protected] mailto:[email protected]>
> > > Sent: Tuesday, October 31, 2023 6:53 AM
> > > To: SprinklerForum <[email protected] 
> > > mailto:[email protected]>
> > > Subject: [Sprinklerforum] Pressure Regulating Valves Residual Pressures
> > > 
> > >  
> > > 
> > > Good morning, Forum!  I hope everyone is having a great week!!  
> > > 
> > >  
> > > 
> > > I think I got this right, but someone is questioning me.  I have an 
> > > automatic standpipe with factory pressure-regulating valves (i.e., Zurn 
> > > 4000).  When calculating residual pressures at the inlet of the PRV to be 
> > > used in the sizing charts, the question is, how much water should I be 
> > > flowing in the system?  One suggestion is only flowing 250 gpm at the 
> > > hose valve you are sizing.  The other suggestion is flowing the system 
> > > demand flow per NFPA 14.  In this case, that would be 750 gpm (250 gpm at 
> > > each of the two most remote hose valves plus 250 gpm at the top of the 
> > > only other standpipe).  We are in agreement that the calculation should 
> > > be a source calc to determine the actual pressure provided by the system.
> > > 
> > >  
> > > 
> > > Thank you,
> > > 
> > > Micah Davis
> > > 
> > > Ferguson Fire Design
> > > 
> > > 
> > > _________________________________________________________
> > > SprinklerForum mailing list:
> > > https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> > >  
> > > https://urldefense.com/v3/__https:/lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org__;!!Ba8_KKAT!Kd8DM2LZyWcEocYD3fg3JDRWY4EbJccNoJAO5nUwJLrU7pZ1PertiR4yFJWGSKkoUpznUXzAlJwSH_Xv107ezuPG$
> > > To unsubscribe send an email to 
> > > [email protected] 
> > > mailto:[email protected]
> > > 
> > 
> > 
> > _________________________________________________________
> > SprinklerForum mailing list:
> > https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org 
> > https://urldefense.com/v3/__https:/lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org__;!!Ba8_KKAT!Kd8DM2LZyWcEocYD3fg3JDRWY4EbJccNoJAO5nUwJLrU7pZ1PertiR4yFJWGSKkoUpznUXzAlJwSH_Xv107ezuPG$
> > To unsubscribe send an email to 
> > [email protected] 
> > mailto:[email protected]
> > 
> 
>  
> 
>  
> 
> --
> 
> Greg McGahan
> 
> Genesis Fire Services, LLC
> 
> 4912 Glover Lane. Milton, FL 32570
> 
> P- 850-637-8535 tel:850-637-8535
> 
> C- 850-712-9555 tel:850-712-9555
> 
> 
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to [email protected]
> 
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to