The requirements of NFPA-14 for the standpipe hose valves are maximum 175-psi 
static outlet pressure and minimum 100-psi residual outlet pressure while 
flowing 250-gpm through the hose valve. 
If your pump source is from the city mains, then make it easy on yourself and 
select a PRV hose valve that will provide maximum 165-psi static outlet 
pressure. 
This should allow you to use whatever residual inlet pressure while flowing the 
750-gpm total standpipe demand and still provide the minimum 100-psi residual 
outlet pressure. 

I used the 165-psi static outlet pressure cause the pump inlet pressure may 
vary up/down which will vary the pump static outlet pressure which may raise 
the static outlet pressure over 175-psi. 

If the pump source has a constant pressure like an elevated tank, then select a 
PRV that will provide a maximum 175-psi outlet pressure. 

Just my opinion but if you select a PRV based on the maximum static outlet 
pressure then this should allow a bit more than the 100-psi minimum outlet 
pressure. Check the charts to verify this. 
Don’t select a PRV based on providing just the minimum outlet pressure. 
I think that the fire department will appreciate any extra pressure to offset 
the friction loss through their fire hoses.
Rick Matsuda

> On Oct 31, 2023, at 7:24 AM, Eric Rieve <[email protected]> wrote:
> 
> 
> Micah,
>  
> Looking at the spec sheet from Zurn I agree with Travis that you use your 
> expected residual pressure while flowing the full system demand of 750gpm. I 
> haven’t installed this valve myself, but you’ll notice on the residual 
> pressure charts that the bonnet type curve lines stop well below 175psi. So, 
> while you may pick a 120psi outlet pressure while flowing 750gpm, the extra 
> play in the curve should allow the valve to maintain an outlet pressure below 
> 175psi when being tested individually at 250gpm.
>  
> Hope this helps!
> Eric Rieve, SET
> Rieve Fire Protection
>  
> From: Micah Davis <[email protected]> 
> Sent: Tuesday, October 31, 2023 6:53 AM
> To: SprinklerForum <[email protected]>
> Subject: [Sprinklerforum] Pressure Regulating Valves Residual Pressures
>  
> Good morning, Forum!  I hope everyone is having a great week!!  
>  
> I think I got this right, but someone is questioning me.  I have an automatic 
> standpipe with factory pressure-regulating valves (i.e., Zurn 4000).  When 
> calculating residual pressures at the inlet of the PRV to be used in the 
> sizing charts, the question is, how much water should I be flowing in the 
> system?  One suggestion is only flowing 250 gpm at the hose valve you are 
> sizing.  The other suggestion is flowing the system demand flow per NFPA 14.  
> In this case, that would be 750 gpm (250 gpm at each of the two most remote 
> hose valves plus 250 gpm at the top of the only other standpipe).  We are in 
> agreement that the calculation should be a source calc to determine the 
> actual pressure provided by the system.
>  
> Thank you,
> Micah Davis
> Ferguson Fire Design
> 
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to [email protected]
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to