Well, they can’t have a minimum of 100 psi AND a maximum of 100 psi available 
at the hose valve. So, if they want to limit the residual pressure to a maximum 
of 100 psi, then they need to deviate from NFPA 14 and allow LESS THAN 100 psi 
as the minimum.

[Note: I suppose that maybe you could utilize a pilot-operated 
pressure-regulating valve at every hose valve location to keep the pressure 
right at 100 psi over a wide range of flow, but that would be unorthodox to say 
the least.]

Kyle Montgomery
 [cid:[email protected]]
Aero Automatic Sprinkler Co.
21605 N. Central Ave.
Phoenix, AZ 85024
Direct: 623.580.7820
Cell: 602.763.4736
[email protected]<mailto:[email protected]>



From: Greg McGahan <[email protected]>
Sent: Tuesday, October 31, 2023 9:16 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [EXTERNAL] [Sprinklerforum] Re: Pressure Regulating Valves Residual 
Pressures

With all due respect Rick, I have had Fire Departments very concerned about the 
residual pressure being greater than 100 psi for safety. Sizing PRV's is not 
the easiest part of a standpipe design. If you are in a jurisdiction that 
requires

With all due respect Rick, I have had Fire Departments very concerned about the 
residual pressure being greater than 100 psi for safety.

Sizing PRV's is not the easiest part of a standpipe design. If you are in a 
jurisdiction that requires flow testing and recording the pressures prior to 
the final inspection (as it should be per NFPA 14), guessing could cost a lot 
of money to correct.

On Tue, Oct 31, 2023 at 10:49 AM Rick Matsuda 
<[email protected]<mailto:[email protected]>> wrote:
The requirements of NFPA-14 for the standpipe hose valves are maximum 175-psi 
static outlet pressure and minimum 100-psi residual outlet pressure while 
flowing 250-gpm through the hose valve.
If your pump source is from the city mains, then make it easy on yourself and 
select a PRV hose valve that will provide maximum 165-psi static outlet 
pressure.
This should allow you to use whatever residual inlet pressure while flowing the 
750-gpm total standpipe demand and still provide the minimum 100-psi residual 
outlet pressure.

I used the 165-psi static outlet pressure cause the pump inlet pressure may 
vary up/down which will vary the pump static outlet pressure which may raise 
the static outlet pressure over 175-psi.

If the pump source has a constant pressure like an elevated tank, then select a 
PRV that will provide a maximum 175-psi outlet pressure.

Just my opinion but if you select a PRV based on the maximum static outlet 
pressure then this should allow a bit more than the 100-psi minimum outlet 
pressure. Check the charts to verify this.
Don’t select a PRV based on providing just the minimum outlet pressure.
I think that the fire department will appreciate any extra pressure to offset 
the friction loss through their fire hoses.
Rick Matsuda


On Oct 31, 2023, at 7:24 AM, Eric Rieve 
<[email protected]<mailto:[email protected]>> wrote:

Micah,

Looking at the spec sheet from Zurn I agree with Travis that you use your 
expected residual pressure while flowing the full system demand of 750gpm. I 
haven’t installed this valve myself, but you’ll notice on the residual pressure 
charts that the bonnet type curve lines stop well below 175psi. So, while you 
may pick a 120psi outlet pressure while flowing 750gpm, the extra play in the 
curve should allow the valve to maintain an outlet pressure below 175psi when 
being tested individually at 250gpm.

Hope this helps!
Eric Rieve, SET
Rieve Fire Protection

From: Micah Davis <[email protected]<mailto:[email protected]>>
Sent: Tuesday, October 31, 2023 6:53 AM
To: SprinklerForum 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Pressure Regulating Valves Residual Pressures

Good morning, Forum!  I hope everyone is having a great week!!

I think I got this right, but someone is questioning me.  I have an automatic 
standpipe with factory pressure-regulating valves (i.e., Zurn 4000).  When 
calculating residual pressures at the inlet of the PRV to be used in the sizing 
charts, the question is, how much water should I be flowing in the system?  One 
suggestion is only flowing 250 gpm at the hose valve you are sizing.  The other 
suggestion is flowing the system demand flow per NFPA 14.  In this case, that 
would be 750 gpm (250 gpm at each of the two most remote hose valves plus 250 
gpm at the top of the only other standpipe).  We are in agreement that the 
calculation should be a source calc to determine the actual pressure provided 
by the system.

Thank you,
Micah Davis
Ferguson Fire Design

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://urldefense.com/v3/__https:/lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org__;!!Ba8_KKAT!Kd8DM2LZyWcEocYD3fg3JDRWY4EbJccNoJAO5nUwJLrU7pZ1PertiR4yFJWGSKkoUpznUXzAlJwSH_Xv107ezuPG$>
To unsubscribe send an email to 
[email protected]<mailto:[email protected]>

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://urldefense.com/v3/__https:/lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org__;!!Ba8_KKAT!Kd8DM2LZyWcEocYD3fg3JDRWY4EbJccNoJAO5nUwJLrU7pZ1PertiR4yFJWGSKkoUpznUXzAlJwSH_Xv107ezuPG$>
To unsubscribe send an email to 
[email protected]<mailto:[email protected]>


--
Greg McGahan
Genesis Fire Services, LLC
4912 Glover Lane. Milton, FL 32570
P- 850-637-8535
C- 850-712-9555
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to