Living in the Pacific time zone means that I'm usually late to the party, but 
Kyle just hit on what I was going to add to this conversation.      Per fire 
code, this building has a minimum fire flow requirement of 1,500 gpm with 
reduction for sprinklers, and depending on gross area, it may be more.  I don't 
want to veer too far off topic here, but we have an INSIDIOUS problem with 
water supply deterioration in San Diego and this may well be an endemic issue 
on a broader scale.   When I started in the trade (an era now known as the 
Before Times), much of SoCal's water systems were brand new and the expansion 
of our suburban built environment meant that infrastructure had to be developed 
to facilitate growth, especially in LA, Orange and San Diego Counties.   Many 
of the water systems were commissioned with well over 100 psi static pressures 
and high-high residuals and 6,000 gpm flow capabilities.  These have diminished 
due to increased demand as more and more meters are connected to these zones, 
and also because some of the zones with especially high pressures have actually 
been "turned down" by the systems operators (both muni and private), because 
they found over time that 120 psi residual pressure leads to all sorts of 
surge- and hammer-related fatigue and maintenance issues.

The problem,  as you have here, is that if the owners of properties affected by 
these changes aren't informed by the water purveyors that they now have 40-60 
less psi of working pressure.  No much you can do about organic pressure drops, 
but when the sysop intentionally reduces the pressure and doesn't advise its 
ratepayers...   like, wow.   And this is going on right now in my home region.  
 Try to explain to a property owner that they may have to put in a fire pump 
because the fire official that serves them is holding them accountable for the 
operational strategies of the water department that serves them, and they're 
the SAME municipality.   Seems to me that there's a helluva  bruhaha a' brewing.

Back to this one - if the FD can't draw 1,000 gpm from the public water supply, 
then THAT is what needs to be investigated.   I know that we're all in the 
business of selling work, but there's more than a touch of Stockholm Syndrome 
in the acceptance of this fate by both ownership and the fire protection 
community.   I'm a consultant, so my first advice to this owner would be get a 
stool and take it to city hall and go from department to department - fire, 
water, economic development, city attorney - and get up on that stool and start 
screaming as loudly as possible that this agency or that agency has put them in 
a corner that will cost 6-figures that they've not been reserving in the 
operation of this building.   Even if the owner has religiously kept up an NFPA 
25 ITM program, there would have been NOTHING they could do to mitigate or 
pre-empt this deficiency and it's most certainly not the responsibility of 
private property owners to assure that the water purveyor and serving fire 
department are on same page regarding the delivery of adequate fire flow.

The code hasn't changed, it's the water supply that dropped.   Code says the 
building owner must maintain fire/life safety systems in accordance with codes 
and standards in effect when the building was certified for occupancy, unless 
use and occupancy class change.   Has the occupancy class changed, or is the 
building still being used for what it was originally certified for?   If no 
change, then what I would do (advising the owner as a consultant, or as the 
owner myself) is to respectfully send a letter to the city attorney or city 
manager depending on type of government model, and respectfully decline to 
conform to any notice of correction that I received.   If the building was 
approved with a manual standpipe, and it's still 4-stories high and hasn't 
changed use, then it's still required to have a manual standpipe.     The fire 
official is not empowered to make a code exception and require them to have an 
automatic one and I'd call them on that.    If you want to get involved that's 
your choice, but if you start down this path you are incurring potential 
liability that I personally would not touch.

This sh*t is starting to make me mental...

Steve L.

From: Kyle.Montgomery <[email protected]>
Sent: Monday, July 01, 2024 9:05 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: [External]Re: Water Tank for Standpipe

Agreed. Also, if they can't support a manual standpipe calculation, how are 
they able to support the site fire flow requirements? That's usually at least 
1,000 GPM, and often much greater.

Kyle Montgomery
 [cid:[email protected]]
Aero Automatic Sprinkler Co.
21605 N. Central Ave.
Phoenix, AZ 85024
Direct: 623.580.7820
Cell: 602.763.4736
[email protected]<mailto:[email protected]>



From: Ken Wagoner 
<[email protected]<mailto:[email protected]>>
Sent: Monday, July 1, 2024 8:09 AM
To: 
[email protected]<mailto:[email protected]>
Subject: [External][Sprinklerforum] Re: Water Tank for Standpipe

What Cliff said.

Among the issues I have to suggest you ask is "why" the city supply has 
diminished.  And, as always, I agree with Cliff, it's likely not the 
responsibility of the building owner (school district?) to sort out the "why" 
issues.

hope this helps,
Ken Wagoner, SET
Parsley Consulting
500 West Mechanic Street
Harrisonville, Missouri 64701-2235
Phone: (760) 745-6181
Visit the 
website<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.parsleyconsulting.com%2f&c=E,1,Y5zKJKPEh1mBEBqSR-VE9cUKl5y-eyP8BpvmE_5j9ZqW2eJbNphYzrCMBZ-2YuX6d-RRkHI4gQ1FV-cvOeCfRC58uZS9NiToZv2mx7909oCqLvCW_n5hDHeK&typo=1>


On 7/1/2024 10:03 AM, [email protected]<mailto:[email protected]> wrote:
Hi Brian,

I may be completely off base on this  but, if the city supply can't supply 1000 
gpm to the site and it could at some point in time, it sounds like they have an 
issue with their underground piping.  They need to start looking for a 
partially closed isolation valve in their system.  It's either that or an 
obstruction in their line.  Either way, I don't think it's the building owner's 
responsibility to solve the City's issue.

Cliff Whitfield, SET
President

Fire Design, Inc.
940 Summerbrooke Dr
Tallahassee, FL 32312
Ph: 828-284-4772
[Description: New FDI Logo-4.jpg]

From: Brian Harris <[email protected]><mailto:[email protected]>
Sent: Monday, July 1, 2024 10:57 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]><mailto:[email protected]>
Subject: [Sprinklerforum] Re: Water Tank for Standpipe

Mostly volume, slight pressure.

Thank you,

Brian Harris, CET
BVS Systems Inc.

From: Fpdcdesign <[email protected]<mailto:[email protected]>>
Sent: Monday, July 1, 2024 9:55 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: Water Tank for Standpipe

Volume or pressure?

Todd Williams
Fire Protection Design/Consulting
Stonington, CT
860-608-4559


On Jul 1, 2024 at 9:25 AM, <Brian Harris<mailto:[email protected]>> 
wrote:
Todd-
Yes, it's a manual wet standpipe. Problem is the city supply has dropped a fair 
amount and now the standpipe test won't pass.

Thank you,

Brian Harris, CET
BVS Systems Inc.

From: Fpdcdesign <[email protected]<mailto:[email protected]>>
Sent: Monday, July 1, 2024 9:21 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: Water Tank for Standpipe

Isn't this a 4 story building? Below the high rise threshold, I assume. Can it 
be a manual wet standpipe?

Todd Williams
Fire Protection Design/Consulting
Stonington, CT
860-608-4559



On Jul 1, 2024 at 9:09 AM, <Paul Kimble<mailto:[email protected]>> wrote:
Has anyone done a valued engineering survey of the city water supply and 
compared the original water test provided to the current. Is the city supply a 
gravity fed system or a system utilizing pumps? There may have been a pump down 
when you performed your last test or there maybe valves within the city supply 
that are partially open causing your loss.

Paul D. Kimble
VP Operations
A.S. Barlin Associates, Inc.
[email protected]<mailto:[email protected]>
(973) 696-6601 Office
(973) 632-8341 Cell

From: Eric Rieve <[email protected]<mailto:[email protected]>>
Sent: Monday, July 1, 2024 8:27 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: Water Tank for Standpipe

Brian,

I have the feeling that messing around with something complicated like a 
break-tank and having to rearrange your fire pump wouldn't be worth it compared 
to simply installing a 30-minute duration dry hydrant on the property. It would 
be a lot larger tank but would guarantee you have a dedicated water supply 
volume just for standpipes.

If your city water supply has already lost 25% of it's capacity, trying to 
design a work-around based on the new number is just setting the property up 
for having to go through the entire exercise again when the supply gets even 
worse. Taking the standpipe demand out altogether also benefits the sprinkler 
system's design longevity since you'll have significantly reduced the demand 
going forward.

Just my two cents.

Hope this helps,
Eric Rieve, SET
Rieve Fire Protection

From: Brian Harris <[email protected]<mailto:[email protected]>>
Sent: Monday, July 1, 2024 7:53 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: Water Tank for Standpipe

Travis-
Yes, & yes. My question was since the system was designed and installed the 
water supply now is about 3/4 of what it was. We are looking to supplement the 
city supply with a water tank since the fire truck shuts down before we can get 
the 1000gpm. The city supply is running out of water. I was curious as to the 
sizing of a supplemental tank. I see if it's only supplied by a tank, it needs 
a 30-minute duration. Since the city is capable of supplying "most" of the 
demand I looking for the best way would be to properly size a tank.

Thank you,

Brian Harris, CET
BVS Systems Inc.

From: Travis Mack <[email protected]<mailto:[email protected]>>
Sent: Monday, July 1, 2024 7:45 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: Water Tank for Standpipe

I doubt that school is tall enough to  be a high rise. Manual is allowed per 
NFPA 14. Do you know what a manual standpipe is? If so, contact the AHJ to find 
out what they require you use as a supply value.  A manual standpipe has its 
supply as the FDC. So calculate as the FDC as your supply with the values the 
ahj provides. It's likely going to be something like 150 psi at 1000 gpm.


Travis Mack, SET

M.E.P.CAD |

181 N. Arroyo Grande Blvd. #105 I Henderson, NV 89074

www.mepcad.com<http://www.mepcad.com/> | m: 480.547.9348



AutoSPRINK  |  AutoSPRINK FAB  |  AutoSPRINK RVT  |  AlarmCAD



Book appointment time in my calendar

https://calendly.com/t_mack_mepcad

________________________________
From: Brian Harris <[email protected]<mailto:[email protected]>>
Sent: Monday, July 1, 2024 4:38:05 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: Water Tank for Standpipe


Yasser



Thank you,



Brian Harris, CET

BVS Systems Inc.



From: Yasser Amer Ahmed <[email protected]<mailto:[email protected]>>
Sent: Monday, July 1, 2024 6:44 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: Water Tank for Standpipe



Hi Brian,



As per NFPA-14, 5.2 (2024 Ed.) 5.2 Minimum Supply for Class I, Class D, and 
Class III Systems. The minimum water supply shall be capable of providing the 
system de1nand established by Chapter 10 for at least 30 minutes.



All Gratitude,



Yasser Amer Ahmed

Fire Protection & Plumbing Specialist

Registered Fire Protection Consultant

MBA, LEED AP BD+C(tm), CPD, CFPS, MIFireE, PMSFPE



[cid:[email protected]]



Smart Village, Cairo-Alexandria Desert Road

Street 26, Building 10

P.O. Box: 129, Giza 12577, Egypt

Tel: +202 3531 8000

Fax: +202 3537 1223

dar.com<https://urldefense.proofpoint.com/v2/url?u=http-3A__dar.com_&d=DwMFAg&c=0YGvTs3tT-VMy8_v51yLDw&r=BPv183lhQEq9N7uN6BtSUYy-qO1aQth8MfS3CXy9v8o&m=AwHdiOGHCF__Z72zfS9hXpv57AcrHPsoC4nxS7tvlkY&s=RZxKhKFy24ZwTQD2ONzIVG3oH1WAdGB-GK2L6HoX0Fs&e=>



[cid:[email protected]]<https://urldefense.proofpoint.com/v2/url?u=http-3A__dar.com_&d=DwMFAg&c=0YGvTs3tT-VMy8_v51yLDw&r=BPv183lhQEq9N7uN6BtSUYy-qO1aQth8MfS3CXy9v8o&m=AwHdiOGHCF__Z72zfS9hXpv57AcrHPsoC4nxS7tvlkY&s=RZxKhKFy24ZwTQD2ONzIVG3oH1WAdGB-GK2L6HoX0Fs&e=>

Please consider the environment before printing this document







From: Travis Mack <[email protected]<mailto:[email protected]>>
Sent: Monday, July 1, 2024 1:34 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: Water Tank for Standpipe



! External Email, Use Caution !



Is it a high rise or mid rise? If mid rise, calc it to the FDC and be done. If 
a high rise and automatic standpipe, check NFPA 14. The duration is 30 minutes. 
 So that is how you would size a tank.



Travis Mack, SET

M.E.P.CAD |

181 N. Arroyo Grande Blvd. #105 I Henderson, NV 89074

www.mepcad.com<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.mepcad.com%2f&c=E,1,-4N2RZKUba_tdy65g6bmxh0QKzZyB4IFxh7FewvPS08dfMil9SJ7e-nULD3iv8Tco6tXDK1EfeIYVTl6v8gt_jeh3nwQJShLejhSBFPVdWqVOxQnapv-TMIHA6g,&typo=1>
 | m: 480.547.9348



AutoSPRINK  |  AutoSPRINK FAB  |  AutoSPRINK RVT  |  AlarmCAD



Book appointment time in my calendar

https://calendly.com/t_mack_mepcad



________________________________

From: Brian Harris <[email protected]<mailto:[email protected]>>
Sent: Monday, July 1, 2024 3:31:59 AM
To: 
[email protected]<mailto:[email protected]>
 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Water Tank for Standpipe



We have a project where the water supply has degraded a good bit since 
installation was completed. Sprinkler system and pump test all pass but the 
standpipe test runs out of water. Only thing I can think of to help would be a 
water tank but how would you even size one since the "duration" of a standpipe 
test is open ended? Any other thoughts?



Thank you,



Brian Harris, CET

BVS Systems Inc.

bvssystemsinc.com<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fbvssystemsinc.com%2f&c=E,1,DxViP7dSzV-R2rx5fGIyoL1vsDK_tTbfrJamJJsCEkhMVaCVUXX3uMknt5ksggBpEfXELKFUusTuDEcjOcvs4e1Xf-ZA6si2AAvUiof7pgyIcg,,&typo=1>

Phone: 704.896.9989

Fax: 704.896.1935





________________________________



Confidentiality & Disclaimer Note: This e-mail (including any attachments) 
contain protected and confidential information intended for the sole use of the 
individual or organization addressee. If you are not the addressee or an 
authorized agent acting on their behalf, or if you have received this message 
by error, please notify the sender immediately be returning the message. It 
must not be copied, distributed or used in any other way but should be 
immediately deleted from your system.

While Dar and the Dar Group strive to maintain high standards of communication, 
reliability, authenticity and integrity, neither shall be liable for the 
improper or incomplete transmission of the information contained in this 
communication nor for any delay in its receipt or damage to your system. 
Neither Dar nor the Dar Group guarantees that the integrity of this 
communication has been maintained or that this communication is free of 
viruses, interceptions or interference.

Confidentiality & Disclaimer Note: This e-mail (including any attachments) 
contain protected and confidential information intended for the sole use of the 
individual or organization addressee. If you are not the addressee or an 
authorized agent acting on their behalf, or if you have received this message 
by error, please notify the sender immediately be returning the message. It 
must not be copied, distributed or used in any other way but should be 
immediately deleted from your system. While Dar and the Dar Group strive to 
maintain high standards of communication, reliability, authenticity and 
integrity, neither shall be liable for the improper or incomplete transmission 
of the information contained in this communication nor for any delay in its 
receipt or damage to your system. Neither Dar nor the Dar Group guarantees that 
the integrity of this communication has been maintained or that this 
communication is free of viruses, interceptions or interference.
_________________________________________________________ SprinklerForum 
mailing list: 
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To 
unsubscribe send an email to 
[email protected]<mailto:[email protected]>
_________________________________________________________ SprinklerForum 
mailing list: 
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To 
unsubscribe send an email to 
[email protected]<mailto:[email protected]>

[https://s-install.avcdn.net/ipm/preview/icons/icon-envelope-tick-round-orange-animated-no-repeat-v1.gif]<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>
Virus-free.www.avast.com<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>




_________________________________________________________

SprinklerForum mailing list:

https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org

To unsubscribe send an email to 
[email protected]<mailto:[email protected]>

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to